Ignition 7.9.5 - isAlarmActiveFiltered - wildcards for relative tagpath
Hi @KathyApplebaum,
We try to use the new expression in 7.9.5 isAlarmActiveFiltered
We have gateway tags inside an UDT with the following expression
Tag1 :
forceQuality(isAlarmActiveFiltered("..[.]/*_AH", "*", "*", 3, 3, 0, 1, 0),192)
Tag2 :
forceQuality(isAlarmActive("..[.]/*_AH","*"),192)
We have an active alarm with priority 3,
Tag1 = 0 instead of 1 as expected
Tag2 = 1
Can we use "…[.] " or these kinds of widcards for relative tagPaths in isAlarmActiveFiltered ???
It seem to be mandatory to have a path with an explicit tag provider (as for example “[default]”) in isAlarmActiveFiltered
Hey @mazeyrat,
The provider name is only required in the tagPath on gateway-scoped expressions, otherwise the function assumes the default provider.
The isAlarmActiveFiltered function uses the same tagPathParser that isAlarmActive uses, so wildcards should all work the same way . However, I think the syntax in your example is a bit off. If you’re specifying a provider, it should be the first item in the string.
So in your example it should be something like:
forceQuality(isAlarmActiveFiltered("[.]../*_AH", "*", "*", 3, 3, 0, 1, 0),192)
Yes @Michael.Stofan,
forceQuality(isAlarmActive("[.]../*_AH","*"),192)
is OK,
but is isAlarmActiveFiltered with same TagPath filter criteria of is NOK :frowning:
Hmm… Looks like something may not be working right then. Can you send me an example of one of your UDTs so we can test it out?
@Michael.Stofan
See attached an export of the UDT
Alarme and AlarmeMoyenne are OK
AlarmeHaute is not working.
udt_alarme.xml (1.7 KB)
Hi, I know this is an old converstation, but I have the same problem with realtive paths for isAlarmActiveFiltered in UDT´s. Did anyone of you find a solution for this?
We use with success expression like this (inside UDT on the tag /TS/STATUS)
(Ignition 7.9.12, I suppose OK with 7.9.6+ )
isAlarmActiveFiltered(replace("[default]{PathToTag}*","/TS/STATUS","/TA"), "", "", 3, 3, 0, 1, 0),
OK, Have you tried this script in 8.0.X? it doesn´t seem to work in 8.0
Expression has changed in Ignition 8, especially UDT parameter.
Example for 8 :
isAlarmActiveFiltered(concat("[default]",replace(concat({PathToTag},"*"),"/TS/STATUS","/TA")), "", "", 3, 3, 0, 1, 0),
Thanks!