Monitoring the device load factor
For those not at 8.1.6 yet though, I got this from Travis (modified to be a function).
Bonus points if you can tell me how to get the number of tags subscribed to a Device… or how I can find out how to do this using the SDK doco. I couldn’t see the IgnitionGateway class within the javadocs :frowning:
def getDeviceLoadFactor(deviceName):
	Description:
		Gets the load factors for each Device/PLC and writes these into a dataset tag within each PLC's UDT instances.
	    This function must be called from the gateway context. It will not run in any other context (i.e. Designer or Client)
	Arguments:
		deviceName: the name of the device to get the load factor(s) for
	Return:
		A dictionary of device name and metrics which is a dictionary of scan rates and load factors
	from com.inductiveautomation.ignition.gateway import IgnitionGateway
	import traceback
	context = IgnitionGateway.get()
	dm = context.getModule("com.inductiveautomation.opcua").getClass().getClassLoader().loadClass("com.inductiveautomation.ignition.gateway.opcua.OpcUaModule").server.getDeviceManager()
	deviceObj = dm.getDevice(deviceName)
	metrics = deviceObj.getPollingMetrics().get()
	cr = metrics.concurrentRequests
	rsl = metrics.rateStatsList
	loadFactors = {}
	for r in rsl:
		hg = r.histogram.getMedian() / 1000000
		rq = r.requestCount
		rate = r.rate
		loadFactor = round(((hg * rq / cr) / rate) * 100)
		loadFactors[rate] = loadFactor
	deviceMetrics = {'device': deviceName,
					 'metrics': loadFactors}
	return deviceMetrics