Hi…
Yet another way to pair Ignition with RSLogix Emulate 5000 is: Ignition > OPC-DA > FactoryTalk Gateway > RSlinx Enterprise.
*EDIT: FactoryTalk Gateway must be installed prior to attempting this method.
- In FactoryTalk Administrator set up a new local application with an RSLinx Enterprise Server and a new shortcut pointing to the emulator.
- In Ignition Gateway create a new OPC Server Connection.
• Choose OPC-DA COM Connection;[next] Local; [next] FactoryTalk Gateway
• Name it the same as the shortcut in step 1
• Save changes. - Start emulator, download code, put in run.
- Open Ignition Designer and refresh the OPC Browser. Your connection should show up with all the tags live from the emulator.
As you were,
Steve