# 1756-ENBT with OPC UA

**URL:** <https://forum.inductiveautomation.com/t/1756-enbt-with-opc-ua/1473>\
**Category:** Ignition\
**Created:** [January 31, 2010, 4:39am UTC](https://forum.inductiveautomation.com/t/1756-enbt-with-opc-ua/1473 "2010-01-31T04:39:58Z")\
**Posts on this page:** 14\
**Page:** 1

<div class="post-metadata">

**Author:** ![david\_mccutchen](https://avatars.discourse-cdn.com/v4/letter/d/919ad9/32.png) [@david\_mccutchen](https://forum.inductiveautomation.com/u/david_mccutchen)\
**Post date:** [January 31, 2010, 4:39am UTC](https://forum.inductiveautomation.com/t/1756-enbt-with-opc-ua/1473/1 "2010-01-31T04:39:58Z")

</div>

Your help documentation indicates the PLC5 driver will work with the 1756-ENET module. Will it work with the 1756-ENBT which is far more common? I am having trouble getting this to work with a passthrough to DH+. Maybe its because its not supported?

---

<div class="post-metadata">

**Author:** ![thechtman](https://avatars.discourse-cdn.com/v4/letter/t/e56c9b/32.png) [@thechtman](https://forum.inductiveautomation.com/u/thechtman)\
**Post date:** [February 2, 2010, 6:16pm UTC](https://forum.inductiveautomation.com/t/1756-enbt-with-opc-ua/1473/2 "2010-02-02T18:16:40Z")

</div>

The PLC-5 driver works with the 1756-ENBT and routing through a DHRIO module to DH+. The connection path will look like 1,6,3,60.  
Where:  
1 designates the backplane.  
6 is the slot of the DHRIO module.  
3 is the channel on the DHRIO module. (2 = channel A and 3 = channel B)  
60 is the DH+ node of the PLC5. This is in octal.

What is your path architecture?

---

<div class="post-metadata">

**Author:** ![david\_mccutchen](https://avatars.discourse-cdn.com/v4/letter/d/919ad9/32.png) [@david\_mccutchen](https://forum.inductiveautomation.com/u/david_mccutchen)\
**Post date:** [February 2, 2010, 6:33pm UTC](https://forum.inductiveautomation.com/t/1756-enbt-with-opc-ua/1473/3 "2010-02-02T18:33:06Z")

</div>

Ok, I tried this the other day. For host name I put in the address of the CTRLGX gateway. (Help documentation doesn’t reference this for CTLGX passthrough) and for the connect string I used the same as what you stated. What am I missing?

---

<div class="post-metadata">

**Author:** ![thechtman](https://avatars.discourse-cdn.com/v4/letter/t/e56c9b/32.png) [@thechtman](https://forum.inductiveautomation.com/u/thechtman)\
**Post date:** [February 3, 2010, 12:46am UTC](https://forum.inductiveautomation.com/t/1756-enbt-with-opc-ua/1473/4 "2010-02-03T00:46:01Z")

</div>

So I have a better understanding, what is the IP Address of the ENBT module, what slot is the DHRIO module in and DH+ Node Address of the PLC?

Can you drill down to the PLC-5 using Linx? It should look something like:  
-192.168.1.228, 1756-A7  
[color=#FFFFFF]**[/color]-Backplane, 1756-A7  
[color=#FFFFFF][/color]+00, 1756-L1 LOGIX5550, ControlLX  
[color=#FFFFFF][/color]+01, 1756-ENET  
[color=#FFFFFF]**\_\_\_[/color]02, 1756-ENBT  
[color=#FFFFFF]**[/color]- 06, 1756-DHRIO  
[color=#FFFFFF] **_** [/color]+CH A, Data Highway Plus  
[color=#FFFFFF] **_** [/color]-CH B, Data Highway plus  
[color=#FFFFFF] **** [/color]02, 1756-DHRIO  
[color=#FFFFFF]**\_\_\_\_[/color]60, PLC-5/20E, FUNCTEST

---

<div class="post-metadata">

**Author:** ![david\_mccutchen](https://avatars.discourse-cdn.com/v4/letter/d/919ad9/32.png) [@david\_mccutchen](https://forum.inductiveautomation.com/u/david_mccutchen)\
**Post date:** [February 3, 2010, 3:05pm UTC](https://forum.inductiveautomation.com/t/1756-enbt-with-opc-ua/1473/5 "2010-02-03T15:05:32Z")

</div>

I don’t think we are on the same page. The 1756-ENBT is a stand alone. (No logix processor). It is used as a gateway. (similar to the old pyramid integrators). This is a very common setup in our plant. The connect string is as follows:

`10.24.6.60 = 00, 1756-ENBT/A
          - Backplane = 1756-A7/A
             + 02 = 1756-DHRIO/C
             - 03 = 1756-DHRIO/C
                  - CHA = Datahighway Plus
                      11 = PLC-5/80B`

---

<div class="post-metadata">

**Author:** ![Kyle\_Chase](https://avatars.discourse-cdn.com/v4/letter/k/9de0a6/32.png) [@Kyle\_Chase](https://forum.inductiveautomation.com/u/Kyle_Chase)\
**Post date:** [February 3, 2010, 6:21pm UTC](https://forum.inductiveautomation.com/t/1756-enbt-with-opc-ua/1473/6 "2010-02-03T18:21:17Z")

</div>

So if you wanted to connect to ZL03\_P51, your connection string would be 1,3,2,3

---

<div class="post-metadata">

**Author:** ![david\_mccutchen](https://avatars.discourse-cdn.com/v4/letter/d/919ad9/32.png) [@david\_mccutchen](https://forum.inductiveautomation.com/u/david_mccutchen)\
**Post date:** [February 3, 2010, 6:38pm UTC](https://forum.inductiveautomation.com/t/1756-enbt-with-opc-ua/1473/7 "2010-02-03T18:38:58Z")

</div>

Yea tried that. It just doesn’t work.

---

<div class="post-metadata">

**Author:** ![thechtman](https://avatars.discourse-cdn.com/v4/letter/t/e56c9b/32.png) [@thechtman](https://forum.inductiveautomation.com/u/thechtman)\
**Post date:** [February 3, 2010, 11:00pm UTC](https://forum.inductiveautomation.com/t/1756-enbt-with-opc-ua/1473/8 "2010-02-03T23:00:15Z")

</div>

The ControlLogix shouldn’t be needed but I’ll test it in-house just to make sure and get back to you.

---

<div class="post-metadata">

**Author:** ![thechtman](https://avatars.discourse-cdn.com/v4/letter/t/e56c9b/32.png) [@thechtman](https://forum.inductiveautomation.com/u/thechtman)\
**Post date:** [February 5, 2010, 1:54am UTC](https://forum.inductiveautomation.com/t/1756-enbt-with-opc-ua/1473/9 "2010-02-05T01:54:38Z")

</div>

I tested without the ControlLogix processor through a ENET and ENBT and both connected and browsed fine.

At this point, do the following to create a log file:

1. In the Configure section of the Ignition Gateway, select Console.
2. Select Levels tab then type in PLC5 and click the Set button.
3. Select “Trace” for the level of the xopc.drivers.allenbradley.PLC5EthernetDriver and ABPLC5ConnectRequest items.
4. Add a PLC 5 device.
5. Email me all the wrapper.log files to [support@inductiveautomation.com](mailto:support@inductiveautomation.com).

Thank you,  
Tom

---

<div class="post-metadata">

**Author:** ![david\_mccutchen](https://avatars.discourse-cdn.com/v4/letter/d/919ad9/32.png) [@david\_mccutchen](https://forum.inductiveautomation.com/u/david_mccutchen)\
**Post date:** [February 5, 2010, 2:50am UTC](https://forum.inductiveautomation.com/t/1756-enbt-with-opc-ua/1473/10 "2010-02-05T02:50:57Z")

</div>

Files have been sent. Are you using the 1756-ENBT ip address for "hostname? That is what I am using.

---

<div class="post-metadata">

**Author:** ![david\_mccutchen](https://avatars.discourse-cdn.com/v4/letter/d/919ad9/32.png) [@david\_mccutchen](https://forum.inductiveautomation.com/u/david_mccutchen)\
**Post date:** [February 8, 2010, 5:46pm UTC](https://forum.inductiveautomation.com/t/1756-enbt-with-opc-ua/1473/11 "2010-02-08T17:46:04Z")

</div>

Any progress on this?

---

<div class="post-metadata">

**Author:** ![thechtman](https://avatars.discourse-cdn.com/v4/letter/t/e56c9b/32.png) [@thechtman](https://forum.inductiveautomation.com/u/thechtman)\
**Post date:** [February 9, 2010, 6:57pm UTC](https://forum.inductiveautomation.com/t/1756-enbt-with-opc-ua/1473/12 "2010-02-09T18:57:37Z")

</div>

Sorry for the slow response on this issue.

Question: How many data files is the PLC 5/80 B at station 11 configured for?

I looked at your log files and did some testing and the only thing I found was when I tested with a large number of data files (999) and the browse timed out. If you have a large number of data files, try increasing the Browse Timeout to say 60000 in the device configuration for the PLC 5/80 B. It will also take awhile to collect the browse data in this situation.

---

<div class="post-metadata">

**Author:** ![david\_mccutchen](https://avatars.discourse-cdn.com/v4/letter/d/919ad9/32.png) [@david\_mccutchen](https://forum.inductiveautomation.com/u/david_mccutchen)\
**Post date:** [February 9, 2010, 7:12pm UTC](https://forum.inductiveautomation.com/t/1756-enbt-with-opc-ua/1473/13 "2010-02-09T19:12:19Z")

</div>

I still get the following error(s) when set at 60000 for browse timeout. I am using 10.24.6.60 in the hostname box and have 1,3,2,11 for connect string. See pic above.

`ERROR [PLC5EthernetDriver] [13:04:38,203]: [L11Batchoff] Invalid DHRIO module channel number in path - 1,3,2,11.
INFO | jvm 1 | 2010/02/09 13:04:38 | ERROR [AbstractEthernetDriver$SelectionManager] [13:04:38,203]: Error during NIO selection.
INFO | jvm 1 | 2010/02/09 13:04:38 | java.lang.NullPointerException
INFO | jvm 1 | 2010/02/09 13:04:38 | at com.inductiveautomation.xopc.drivers.allenbradley.requests.ABPLC5ConnectRequest.<init>(ABPLC5ConnectRequest.java:34)
INFO | jvm 1 | 2010/02/09 13:04:38 | at com.inductiveautomation.xopc.drivers.allenbradley.PLC5EthernetDriver.createConnectRequests(PLC5EthernetDriver.java:110)
INFO | jvm 1 | 2010/02/09 13:04:38 | at com.inductiveautomation.xopc.driver.api.AbstractEthernetDriver.channelConnectDone(AbstractEthernetDriver.java:165)
INFO | jvm 1 | 2010/02/09 13:04:38 | at com.inductiveautomation.xopc.driver.api.AbstractEthernetDriver$SelectionManager.run(AbstractEthernetDriver.java:512)
INFO | jvm 1 | 2010/02/09 13:04:38 | at java.lang.Thread.run(Unknown Source)`

---

<div class="post-metadata">

**Author:** ![david\_mccutchen](https://avatars.discourse-cdn.com/v4/letter/d/919ad9/32.png) [@david\_mccutchen](https://forum.inductiveautomation.com/u/david_mccutchen)\
**Post date:** [February 17, 2010, 1:51pm UTC](https://forum.inductiveautomation.com/t/1756-enbt-with-opc-ua/1473/14 "2010-02-17T13:51:14Z")

</div>

Anything new on this?