Are the new Allen Bradley 1756-L8x processors supported for OPCUA comms?

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [February 11, 2016, 4:38pm UTC](https://forum.inductiveautomation.com/t/ab-1756-l8x-processor-support/11199/2 "2016-02-11T16:38:17Z")

</div>

Rockwell changed something in the firmware, so we had to make a change to accommodate… The change should land in the next versions of 7.7 and 7.8.

---

<div class="post-metadata">

**Author:** ![Tim](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/tim/32/3361_2.png) [@Tim](https://forum.inductiveautomation.com/u/Tim)\
**Post date:** [February 11, 2016, 5:04pm UTC](https://forum.inductiveautomation.com/t/ab-1756-l8x-processor-support/11199/3 "2016-02-11T17:04:32Z")

</div>

Is the change needed only for the L8 hardware or for the v28 firmware (which can also run on L7 processors)?

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [February 11, 2016, 5:12pm UTC](https://forum.inductiveautomation.com/t/ab-1756-l8x-processor-support/11199/4 "2016-02-11T17:12:25Z")

</div>

I don’t know, at the time I was testing firmware v28 it was only available for the L8x series.

---

<div class="post-metadata">

**Author:** ![Curlyandshemp](https://avatars.discourse-cdn.com/v4/letter/c/bcef8e/32.png) [@Curlyandshemp](https://forum.inductiveautomation.com/u/Curlyandshemp)\
**Post date:** [February 14, 2016, 9:04pm UTC](https://forum.inductiveautomation.com/t/ab-1756-l8x-processor-support/11199/5 "2016-02-14T21:04:29Z")

</div>

> [@Tim](#):
>
> Are the new Allen Bradley 1756-L8x processors supported for OPCUA comms?

I got caught with this issue last month.  
V7.7.7 has the update to support V28