I have many equipment with trip status Signals.  
Currently, when I receive “Trip” field signal, it generate “Equipment Tripped” alarm in alarm table.  
And, also my equipment icon shows Yellow color and blinking.

Now, I would like to implement as follow;  
If the generated alarm is acknowledged, equipment icon shows Yellow color and NOT blinking.  
If the generated alarm is NOT acknowledged, equipment icon shows Yellow color and blinking.  
[Note: Yellow Color and Blinking for the equipment ICONs, not alarm Rows.]

Any suggestions toward this implementation will be much appreciated.

Thank you.

---

<div class="post-metadata">

**Author:** ![MMaynard](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/mmaynard/32/3366_2.png) [@MMaynard](https://forum.inductiveautomation.com/u/MMaynard)\
**Post date:** [July 15, 2019, 4:03pm UTC](https://forum.inductiveautomation.com/t/acknowledged-alarm-query/26553/2 "2019-07-15T16:03:47Z")

</div>

[https://docs.inductiveautomation.com/display/DOC79/Alarm+Row+Style+Customizer](https://docs.inductiveautomation.com/display/DOC79/Alarm+Row+Style+Customizer)  
For the alarm status page.  
For your equipment icons, just do a custom property evaluating the status and returning an integer.  
Then use the integer returned to set the background color of the control.

---

<div class="post-metadata">

**Author:** ![leo\_amm](https://avatars.discourse-cdn.com/v4/letter/l/9d8465/32.png) [@leo\_amm](https://forum.inductiveautomation.com/u/leo_amm)\
**Post date:** [July 16, 2019, 1:20am UTC](https://forum.inductiveautomation.com/t/acknowledged-alarm-query/26553/3 "2019-07-16T01:20:20Z")

</div>

Hi, how do i evaluate the alarm status for the individual “received Tripped Signal”?

\*\*\*I found my way using the tag change script, Thank you for pointing me to the right direction :D.