# Adding tags on v8 designer launcher

**URL:** <https://forum.inductiveautomation.com/t/adding-tags-on-v8-designer-launcher/28916>\
**Category:** Ignition Early Access\
**Created:** [October 8, 2019, 1:35pm UTC](https://forum.inductiveautomation.com/t/adding-tags-on-v8-designer-launcher/28916 "2019-10-08T13:35:26Z")\
**Posts on this page:** 14\
**Page:** 1

<div class="post-metadata">

**Author:** ![serenaz](https://avatars.discourse-cdn.com/v4/letter/s/4af34b/32.png) [@serenaz](https://forum.inductiveautomation.com/u/serenaz)\
**Post date:** [October 8, 2019, 1:35pm UTC](https://forum.inductiveautomation.com/t/adding-tags-on-v8-designer-launcher/28916/1 "2019-10-08T13:35:26Z")

</div>

I set up a Production Automation Direct 1000 PLC to generate some random data in productivity suite, with tags: Random1, Random2, Random3. I was able to configure this device as ModBus TCP on ignition 8 and the server shows it’s connected. However, when I try to look for tags created in the pro suite, “Random1”, “Random2”, and “Random3” don’t show up on the drop list.

 ![Capture](https://us1.discourse-cdn.com/inductiveautomation/original/2X/5/554690a34d88a2b5ea7573e15f407c13d1176912.jpeg)

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [October 8, 2019, 1:41pm UTC](https://forum.inductiveautomation.com/t/adding-tags-on-v8-designer-launcher/28916/2 "2019-10-08T13:41:26Z")

</div>

The Modbus protocol has no notion of browsing or tag enumeration. You have create and manually address OPC tags in the designer for every tag in the controller you want to subscribe to. Somewhere in the PLC programming software you should be able to map variables to registers, or get the mapped register if it happens automatically. Then you can make a tag in Ignition using the Modbus addressing syntax: [https://docs.inductiveautomation.com/display/DOC80/Modbus+Addressing](https://docs.inductiveautomation.com/display/DOC80/Modbus+Addressing)

---

<div class="post-metadata">

**Author:** ![serenaz](https://avatars.discourse-cdn.com/v4/letter/s/4af34b/32.png) [@serenaz](https://forum.inductiveautomation.com/u/serenaz)\
**Post date:** [October 8, 2019, 2:18pm UTC](https://forum.inductiveautomation.com/t/adding-tags-on-v8-designer-launcher/28916/3 "2019-10-08T14:18:13Z")

</div>

@Kevin.Herron

I

 ![Capture](https://us1.discourse-cdn.com/inductiveautomation/original/2X/2/28052eb9167cb93386adc4a3576cf061a4a8576c.jpeg)  
 ![Capture2](https://us1.discourse-cdn.com/inductiveautomation/original/2X/b/bbc46ee3d8b8a57813206877c70d546d0ffff2e0.jpeg)  
 ![Capture3](https://us1.discourse-cdn.com/inductiveautomation/original/2X/9/9ece9fb83e5843bcba9fa8419ab9960a54424329.jpeg)

I assigned Modbus Addresses to tags. However I still get an error after I manually address the OPC Item Path.

---

<div class="post-metadata">

**Author:** ![serenaz](https://avatars.discourse-cdn.com/v4/letter/s/4af34b/32.png) [@serenaz](https://forum.inductiveautomation.com/u/serenaz)\
**Post date:** [October 8, 2019, 2:26pm UTC](https://forum.inductiveautomation.com/t/adding-tags-on-v8-designer-launcher/28916/4 "2019-10-08T14:26:14Z")

</div>

The OPC Item Path is [P1-540]HR400001.

In the picture I missed a 0.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [October 8, 2019, 2:48pm UTC](https://forum.inductiveautomation.com/t/adding-tags-on-v8-designer-launcher/28916/5 "2019-10-08T14:48:11Z")

</div>

Leave off the ‘4’ in the OPC Item Path and just try `[P1-540]HR1` etc…

---

<div class="post-metadata">

**Author:** ![serenaz](https://avatars.discourse-cdn.com/v4/letter/s/4af34b/32.png) [@serenaz](https://forum.inductiveautomation.com/u/serenaz)\
**Post date:** [October 8, 2019, 4:09pm UTC](https://forum.inductiveautomation.com/t/adding-tags-on-v8-designer-launcher/28916/6 "2019-10-08T16:09:21Z")

</div>

I tried 1, 401, 4001, 40001, 400001, and none works. Also tried other tags with different addresses. I changed the Modbus server settings to “map value to a single 16 bit Modbus register” in productivity suite. Just shows: value: bad

---

<div class="post-metadata">

**Author:** ![paul-griffith](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/paul-griffith/32/37249_2.png) [@paul-griffith](https://forum.inductiveautomation.com/u/paul-griffith)\
**Post date:** [October 8, 2019, 4:24pm UTC](https://forum.inductiveautomation.com/t/adding-tags-on-v8-designer-launcher/28916/7 "2019-10-08T16:24:18Z")

</div>

![image](https://us1.discourse-cdn.com/inductiveautomation/original/2X/8/81d6796b2dbb59b7100e844a4571ed256d6c2ffe.png)  
Is that `1` a UnitID? Try `[P1-540]1.HR1`, meaning "holding register 1 from unit/slave ID 1 on device `P1-540`"

---

<div class="post-metadata">

**Author:** ![serenaz](https://avatars.discourse-cdn.com/v4/letter/s/4af34b/32.png) [@serenaz](https://forum.inductiveautomation.com/u/serenaz)\
**Post date:** [October 8, 2019, 5:36pm UTC](https://forum.inductiveautomation.com/t/adding-tags-on-v8-designer-launcher/28916/8 "2019-10-08T17:36:45Z")

</div>

@paul-griffith No it’s actually rows and columns of the array I created ☹

---

<div class="post-metadata">

**Author:** ![Paul.Scott](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/paul.scott/32/4578_2.png) [@Paul.Scott](https://forum.inductiveautomation.com/u/Paul.Scott)\
**Post date:** [October 8, 2019, 7:30pm UTC](https://forum.inductiveautomation.com/t/adding-tags-on-v8-designer-launcher/28916/9 "2019-10-08T19:30:08Z")

</div>

> [@serenaz](#):
>
> P1-540

It's silly of me to ask, but just to clarify, what is the name of the device connection on your gateway? Is it `P1-540`, or is it the `p1000_random_test2` device highlighted in your first post?

---

<div class="post-metadata">

**Author:** ![serenaz](https://avatars.discourse-cdn.com/v4/letter/s/4af34b/32.png) [@serenaz](https://forum.inductiveautomation.com/u/serenaz)\
**Post date:** [October 8, 2019, 7:42pm UTC](https://forum.inductiveautomation.com/t/adding-tags-on-v8-designer-launcher/28916/10 "2019-10-08T19:42:48Z")

</div>

@Paul.Scott Good catch! I had them under different names before. But all the folders and devices now have the same name as the device added in the gateway. I changed them when I was testing out the OPC Item Path.

---

<div class="post-metadata">

**Author:** ![serenaz](https://avatars.discourse-cdn.com/v4/letter/s/4af34b/32.png) [@serenaz](https://forum.inductiveautomation.com/u/serenaz)\
**Post date:** [October 9, 2019, 3:50pm UTC](https://forum.inductiveautomation.com/t/adding-tags-on-v8-designer-launcher/28916/11 "2019-10-09T15:50:28Z")

</div>

@Kevin.Herron

I have the same device configuration and OPC Item Path setting for the P1000 device in both v7 and v8. The tags work and update on 7.9, but do not work on 8.0.4. Below are pictures of the settings.  
 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/2X/3/3dfe05289747f25da13810ba6de4acbc697029ad.png)  
Tags and paths in 7.9.

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/2X/7/76e2315e4d7db2d08ebcf9d35dab21f71ed44ad0.png)  
Tags and path in 8.0.4. The value is invalid. Gives message: error\_configuration. when click on the question mark.  
 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/2X/1/1d1dc40977a950b3d6826ba3a71700f418d08f85.png)  
Devices – OPC-UA Server configuration page. Edit device. 7.9 setting

---

<div class="post-metadata">

**Author:** ![serenaz](https://avatars.discourse-cdn.com/v4/letter/s/4af34b/32.png) [@serenaz](https://forum.inductiveautomation.com/u/serenaz)\
**Post date:** [October 9, 2019, 3:51pm UTC](https://forum.inductiveautomation.com/t/adding-tags-on-v8-designer-launcher/28916/12 "2019-10-09T15:51:01Z")

</div>

@Kevin.Herron

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/2X/4/40f97375d7bcc0c292bd3af3acd1f588f6a39f2d.png)  
Devices – OPC-UA Server configuration page. Edit device. 7.9 Advanced setting  
 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/2X/b/b922cdb508ea6a216177fd20510df9bb8413dc12.png)  
Device Connections – OPC UA configuration page. Edit device. 8.0.4 setting  
 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/2X/e/eeb45ff0cddd74ed6a5a2d35563de72767caf817.png)  
Device Connections – OPC UA configuration page. Edit device. 8.0.4 advanced setting

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [October 9, 2019, 3:53pm UTC](https://forum.inductiveautomation.com/t/adding-tags-on-v8-designer-launcher/28916/13 "2019-10-09T15:53:58Z")

</div>

Is the OPC Server name correct?

If you did a fresh install of Ignition 8 the default name is slightly different. “Ignition OPC UA Server” without the hyphen.

---

<div class="post-metadata">

**Author:** ![serenaz](https://avatars.discourse-cdn.com/v4/letter/s/4af34b/32.png) [@serenaz](https://forum.inductiveautomation.com/u/serenaz)\
**Post date:** [October 9, 2019, 4:02pm UTC](https://forum.inductiveautomation.com/t/adding-tags-on-v8-designer-launcher/28916/14 "2019-10-09T16:02:17Z")

</div>

@Kevin.Herron  
Oh my gosh, that solved the problem! I noticed it before but when I hit commit, the OPC server doesn’t change. I went in and manually took out the hyphen this time, now everything is working! Thank you so much.