# Alarm Acknowledge

**URL:** <https://forum.inductiveautomation.com/t/alarm-acknowledge/7773>\
**Category:** Ignition\
**Created:** [January 1, 2014, 4:54am UTC](https://forum.inductiveautomation.com/t/alarm-acknowledge/7773 "2014-01-01T04:54:21Z")\
**Posts on this page:** 2\
**Page:** 1

<div class="post-metadata">

**Author:** ![rwalker1312](https://avatars.discourse-cdn.com/v4/letter/r/9f8e36/32.png) [@rwalker1312](https://forum.inductiveautomation.com/u/rwalker1312)\
**Post date:** [January 1, 2014, 4:54am UTC](https://forum.inductiveautomation.com/t/alarm-acknowledge/7773/1 "2014-01-01T04:54:21Z")

</div>

Is there a way to tie an OPC tag to the alarm Acknowledge on the alarm table? Any help is greatly appreciated

---

<div class="post-metadata">

**Author:** ![anna](https://avatars.discourse-cdn.com/v4/letter/a/779978/32.png) [@anna](https://forum.inductiveautomation.com/u/anna)\
**Post date:** [January 2, 2014, 11:48pm UTC](https://forum.inductiveautomation.com/t/alarm-acknowledge/7773/2 "2014-01-02T23:48:07Z")

</div>

There is currently no way to do this using the built-in “Acknowledge” button. You could, however, make your own button based the “selectedAlarms” dataset of the Alarm Status table. The button would acknowledge the selected alarms and write to the tag(s) as you need.