Hello,

I want to define an alarm. I have a boolean tag. Value 1 is coming. I just want an alarm to come when it is 0 out of 1.

Not when it is equal to 0.

I want an alarm to sound when there is a falling edge from 1 to 0.

Thank you

---

<div class="post-metadata">

**Author:** ![justinedwards.jle](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/justinedwards.jle/32/37854_2.png) [@justinedwards.jle](https://forum.inductiveautomation.com/u/justinedwards.jle)\
**Post date:** [January 24, 2023, 1:53pm UTC](https://forum.inductiveautomation.com/t/alarm-configuration/68955/2 "2023-01-24T13:53:20Z")

</div>

Set your mode to not equal to 1:  
 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/e/e/eedba1cb13bcb1f466a7ba922766a351d132f1e8.png)

Then, trigger your alarm sound off of the Active and Unacknowledged [alarm state](https://docs.inductiveautomation.com/display/DOC81/Alarming):  
 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/3/c/3cae85ace7ed6fefb1b4c51880aceccb722fd456.png)