# Alarm Notification Pipelines - Continuous Notifications

**URL:** <https://forum.inductiveautomation.com/t/alarm-notification-pipelines-continuous-notifications/106065>\
**Category:** Ignition\
**Tags:** ignition81\
**Created:** [May 8, 2025, 4:33pm UTC](https://forum.inductiveautomation.com/t/alarm-notification-pipelines-continuous-notifications/106065 "2025-05-08T16:33:39Z")\
**Posts on this page:** 5\
**Page:** 1

<div class="post-metadata">

**Author:** ![dwb](https://avatars.discourse-cdn.com/v4/letter/d/9dc877/32.png) [@dwb](https://forum.inductiveautomation.com/u/dwb)\
**Post date:** [May 8, 2025, 4:33pm UTC](https://forum.inductiveautomation.com/t/alarm-notification-pipelines-continuous-notifications/106065/1 "2025-05-08T16:33:39Z")

</div>

Hi,

I am using Ignition 8.1.48. There is a tag that, when it is TRUE, should send an email, and if it remains TRUE, it should keep sending an email every minute. However, when the tag value drops to FALSE, it should stop sending emails.  
What is happening is this: Although the tag drops from TRUE to FALSE, I continue receiving emails. I don't know why this is happening.  
Please see the pictures showing my configuration:

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/a/6/a624c1a7e032267b6e41ed3c28d4d793dc77febb.png)

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/d/1/d1af652a96cc420cf344a1d59253d58704beb6bb.png)

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/7/1/714ebbdba593b76f214caedf9c012d4117dce155.png)

Thank you.

---

<div class="post-metadata">

**Author:** ![kvane](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kvane/32/22228_2.png) [@kvane](https://forum.inductiveautomation.com/u/kvane)\
**Post date:** [May 9, 2025, 6:15pm UTC](https://forum.inductiveautomation.com/t/alarm-notification-pipelines-continuous-notifications/106065/2 "2025-05-09T18:15:50Z")

</div>

The alarm in your screenshot is currently configured to fire when a Boolean is False (Equal 0).

You want it Equal to 1 if you want the alarm to be active when the Boolean is True.

---

<div class="post-metadata">

**Author:** ![dwb](https://avatars.discourse-cdn.com/v4/letter/d/9dc877/32.png) [@dwb](https://forum.inductiveautomation.com/u/dwb)\
**Post date:** [May 12, 2025, 1:20pm UTC](https://forum.inductiveautomation.com/t/alarm-notification-pipelines-continuous-notifications/106065/3 "2025-05-12T13:20:19Z")

</div>

Hi,

What is the setting to do this?  
Thanks.

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [May 12, 2025, 1:25pm UTC](https://forum.inductiveautomation.com/t/alarm-notification-pipelines-continuous-notifications/106065/4 "2025-05-12T13:25:52Z")

</div>

In your screenshot, "Setpoint" under Alarm Mode Settings.

---

<div class="post-metadata">

**Author:** ![dwb](https://avatars.discourse-cdn.com/v4/letter/d/9dc877/32.png) [@dwb](https://forum.inductiveautomation.com/u/dwb)\
**Post date:** [June 25, 2025, 7:11pm UTC](https://forum.inductiveautomation.com/t/alarm-notification-pipelines-continuous-notifications/106065/5 "2025-06-25T19:11:14Z")

</div>

Thank you. It worked.