it is possible to set alarms to the “alarm status” component from a Query Tag?

---

<div class="post-metadata">

**Author:** ![Kevin\_Tulloch](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin_tulloch/32/39631_2.png) [@Kevin\_Tulloch](https://forum.inductiveautomation.com/u/Kevin_Tulloch)\
**Post date:** [October 19, 2022, 9:26pm UTC](https://forum.inductiveautomation.com/t/alarm-status-querytag/62566/2 "2022-10-19T21:26:31Z")

</div>

In regards to your concern, you can create alarms within that Query Tag and these alarms will be displayed on the Alarm Status Table component once triggered. Additionally I have included a [link](https://docs.inductiveautomation.com/display/DOC80/Tag+Alarm+Properties#TagAlarmProperties-AlarmPropertyReference) regarding Alarm Property References that you can use to review the differences between Alarm Mode Setting to match your needs.