Regarding the Acknowledge button on the alarm status table, is there a way to have that button write to a tag when pressed? In other words, when Acknowledge is pressed I’d like it to acknowledge the alarm and write to a OPC tag. It doesn’t seem to script like a normal button would. Any ideas?

Many thanks in advance!

Dana

---

<div class="post-metadata">

**Author:** ![Robert.McKenzie](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/robert.mckenzie/32/4134_2.png) [@Robert.McKenzie](https://forum.inductiveautomation.com/u/Robert.McKenzie)\
**Post date:** [December 26, 2013, 11:26pm UTC](https://forum.inductiveautomation.com/t/alarm-status-table-question/7551/2 "2013-12-26T23:26:01Z")

</div>

Absolutely! You just need to write your own alarm acknowledge button. Check out our manual for [system.alarm.acknowledge()](http://www.inductiveautomation.com/support/usermanuals/ignition/system_alarm_acknowledge.htm) and [system.tag.write()](http://www.inductiveautomation.com/support/usermanuals/ignition/system_tag_write.htm).