Ok, I think I'm with you now. You basically want a way to overlay alarm points on the trend of whatever tag raised the alarm (within the PLC).

Of course the alarm tag itself would still be 1 or 0. I agree, trending the alarm tag itself would be rather useless, especially because the alarm journal exists.

The option that I proposed would be a set of _new_ tags within the analog reading UDT (assuming that one exists, which it should). One "alarm value" tag for each alarm that then gets trended. The alarm value is 0 (or, whatever the non-alarm value might be) unless the associated alarm is on.

It would look something like this (blue = analog value, magenta = high alarm value)

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/7/9/7996cba869a8b37f85d4f7c8e6acd04d7172e453.png)

Or, you can trend the alarm setpoint (assuming that it also exists in the UDT) with a fixed, longer logging interval so the operator can see where it crosses the value.

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/e/3/e3cf7a50a67f797db38adbc51c21f63192bb7c24.png)

There's not really a way to put a single point (or a vertical line) on a trend.

I think an "associated trend" property for alarms would be difficult to implement, and is unlikely to happen.

---