# Alarming Status Table

**URL:** <https://forum.inductiveautomation.com/t/alarming-status-table/65969>\
**Category:** Ignition\
**Created:** [November 2, 2022, 5:49am UTC](https://forum.inductiveautomation.com/t/alarming-status-table/65969 "2022-11-02T05:49:28Z")\
**Posts on this page:** 5\
**Page:** 1

<div class="post-metadata">

**Author:** ![Mai\_Watanabe](https://avatars.discourse-cdn.com/v4/letter/m/a87d85/32.png) [@Mai\_Watanabe](https://forum.inductiveautomation.com/u/Mai_Watanabe)\
**Post date:** [November 2, 2022, 5:49am UTC](https://forum.inductiveautomation.com/t/alarming-status-table/65969/1 "2022-11-02T05:49:28Z")

</div>

I have a question about alarming. Using the Alarming Status Table, tags with values greater than the set value are displayed. However, although I have set the Alarm, there are still alarms that I no longer use, and I don't want the alarms that I no longer use to be displayed in the list of Alarming Status Table. Can I select the tags to be displayed in the list in the settings?If so, where can I choose? Also, if I can't select it, do I have to manually remove the alarm from the tag for alarms that I don't use?

---

<div class="post-metadata">

**Author:** ![nminchin](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/nminchin/32/6911_2.png) [@nminchin](https://forum.inductiveautomation.com/u/nminchin)\
**Post date:** [November 2, 2022, 6:23am UTC](https://forum.inductiveautomation.com/t/alarming-status-table/65969/2 "2022-11-02T06:23:43Z")

</div>

If the alarms shouldn't be there anymore, why would you want to keep the alarm configured on the tag? (or keep the tag at all)  
Either remove the alarm from the tag, or disable it on the tag.

---

<div class="post-metadata">

**Author:** ![Mai\_Watanabe](https://avatars.discourse-cdn.com/v4/letter/m/a87d85/32.png) [@Mai\_Watanabe](https://forum.inductiveautomation.com/u/Mai_Watanabe)\
**Post date:** [November 4, 2022, 4:57am UTC](https://forum.inductiveautomation.com/t/alarming-status-table/65969/3 "2022-11-04T04:57:37Z")

</div>

My explanation was insufficient. I am sorry. It is an unnecessary tag for me, but for others (other systems) it is necessary. So I want the GUI I create to show only the alarms for the tags I need.

---

<div class="post-metadata">

**Author:** ![nminchin](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/nminchin/32/6911_2.png) [@nminchin](https://forum.inductiveautomation.com/u/nminchin)\
**Post date:** [November 4, 2022, 5:11am UTC](https://forum.inductiveautomation.com/t/alarming-status-table/65969/4 "2022-11-04T05:11:54Z")

</div>

You haven't mentioned a version or module you're using, but:

- This isn't possible in **Perspective**. You would have to make your own alarm status table and filter it.
- In **Vision** , you can use the `filterAlarm` extension function to post-process alarms and filter out the ones you don't want to see using a lookup table stored somewhere.  
[Vision - Alarm Status Table - Ignition User Manual 8.1 - Ignition Documentation](https://docs.inductiveautomation.com/display/DOC81/Vision+-+Alarm+Status+Table#VisionAlarmStatusTable-ExtensionFunctions)

---

<div class="post-metadata">

**Author:** ![Mai\_Watanabe](https://avatars.discourse-cdn.com/v4/letter/m/a87d85/32.png) [@Mai\_Watanabe](https://forum.inductiveautomation.com/u/Mai_Watanabe)\
**Post date:** [November 4, 2022, 6:58am UTC](https://forum.inductiveautomation.com/t/alarming-status-table/65969/5 "2022-11-04T06:58:39Z")

</div>

I got what I wanted to do! Thank you so much.