<div class="post-metadata">

**Author:** ![Freddy\_Haggblom](https://avatars.discourse-cdn.com/v4/letter/f/ed8c4c/32.png) [@Freddy\_Haggblom](https://forum.inductiveautomation.com/u/Freddy_Haggblom)\
**Post date:** [May 23, 2022, 6:31am UTC](https://forum.inductiveautomation.com/t/alarms-based-on-params/59892/1 "2022-05-23T06:31:28Z")

</div>

Is there any way to separate which alarms should be visible in alarmtable? I have one parent project where I make all design changes(where I have one alarm-table), but for each child project I would like to have separate alarms (different sites) and they should not be able to see eachothers alarms. How do I set this up? 🙂

---

<div class="post-metadata">

**Author:** ![pascal.fragnoud](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pascal.fragnoud/32/24728_2.png) [@pascal.fragnoud](https://forum.inductiveautomation.com/u/pascal.fragnoud)\
**Post date:** [May 23, 2022, 8:00am UTC](https://forum.inductiveautomation.com/t/alarms-based-on-params/59892/2 "2022-05-23T08:00:13Z")

</div>

Set up different alarm journals on your gateway (config → alarming → journal), then use the appropriate journal in each child project.

---

<div class="post-metadata">

**Author:** ![Freddy\_Haggblom](https://avatars.discourse-cdn.com/v4/letter/f/ed8c4c/32.png) [@Freddy\_Haggblom](https://forum.inductiveautomation.com/u/Freddy_Haggblom)\
**Post date:** [May 23, 2022, 10:11am UTC](https://forum.inductiveautomation.com/t/alarms-based-on-params/59892/3 "2022-05-23T10:11:14Z")

</div>

Thank you!

---

<div class="post-metadata">

**Author:** ![andrews](https://avatars.discourse-cdn.com/v4/letter/a/898d66/32.png) [@andrews](https://forum.inductiveautomation.com/u/andrews)\
**Post date:** [May 23, 2022, 2:10pm UTC](https://forum.inductiveautomation.com/t/alarms-based-on-params/59892/4 "2022-05-23T14:10:14Z")

</div>

Adding on to @pascal.fragnoud you will have to filter each alarm journal appropriately. You will have to make sure alarms have something in the path or name you can filter by. Like some sort of site reference. i.e. Site xyz alarmhere and filter with _Site xyz_ or something along those lines.

---

<div class="post-metadata">

**Author:** ![pascal.fragnoud](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pascal.fragnoud/32/24728_2.png) [@pascal.fragnoud](https://forum.inductiveautomation.com/u/pascal.fragnoud)\
**Post date:** [May 23, 2022, 2:30pm UTC](https://forum.inductiveautomation.com/t/alarms-based-on-params/59892/5 "2022-05-23T14:30:17Z")

</div>

He could filter by provider:

![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/6/0/6076586352bf0765e5fb938b8ca85307a38bb130.png)