Your screenshot appears to be of the UDT, not the individual tags, which may have different limits overriding the initial UDT setting.

Also, you mentioned renaming alarms. Did you do this while the alarms were active? Are your logs complaining about unable to acknowledge alarm IDs that dont exist? Have you restarted the gateway? This topic on how to delete alarms may be of help:

> [@How to clear dead alarms from Alarm Journal](https://forum.inductiveautomation.com/t/how-to-clear-dead-alarms-from-alarm-journal/79306):
>
> I deleted some alarm tags when they were active, now the alarm journal show them active all the time. Does anybody know how to reset these alarms?

---