I created an alarm to monitor average % and compare to settings, in this case the average and the setting are both zeros but the alarm is active. This my first attempt with alarms and I can’t figure out what is the cause of this.

 ![](https://us1.discourse-cdn.com/inductiveautomation/original/2X/4/46c821c5ba3d9809e59f6402ffee4e0ebb3fdc9a.png)

---

<div class="post-metadata">

**Author:** ![Duffanator](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/duffanator/32/3560_2.png) [@Duffanator](https://forum.inductiveautomation.com/u/Duffanator)\
**Post date:** [November 9, 2015, 9:07pm UTC](https://forum.inductiveautomation.com/t/alarms/10763/2 "2015-11-09T21:07:38Z")

</div>

Probably because inclusive is set to True in the Alarm Mode Settings section.

Inclusive = True would be \<=  
Inclusive = False would be \<

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [November 9, 2015, 11:47pm UTC](https://forum.inductiveautomation.com/t/alarms/10763/3 "2015-11-09T23:47:27Z")

</div>

[quote=“Jado58”]average and the setting are both zeros but the alarm is active[/quote]You have a 15% deadband defined. So once active, it has to go back above setpoint by the deadband % (or 1/2 the deadband – I can’t remember) in order to reset the alarm. Now, since the setpoint is zero, the deadband is zero, too. So the average going the slightest amount over will reset it.

---

<div class="post-metadata">

**Author:** ![Jado58](https://avatars.discourse-cdn.com/v4/letter/j/cdc98d/32.png) [@Jado58](https://forum.inductiveautomation.com/u/Jado58)\
**Post date:** [November 10, 2015, 3:35pm UTC](https://forum.inductiveautomation.com/t/alarms/10763/4 "2015-11-10T15:35:10Z")

</div>

[quote=“Duffanator”]Probably because inclusive is set to True in the Alarm Mode Settings section.

Inclusive = True would be \<=  
Inclusive = False would be \<[/quote]  
Ah, I was wondering what that was, it solved my issue. Thank you!