# Allen Bradley 1783-NATR, Network Address Translation Router

**URL:** <https://forum.inductiveautomation.com/t/allen-bradley-1783-natr-network-address-translation-router/14515>\
**Category:** Ignition\
**Created:** [June 14, 2017, 1:31pm UTC](https://forum.inductiveautomation.com/t/allen-bradley-1783-natr-network-address-translation-router/14515 "2017-06-14T13:31:00Z")\
**Posts on this page:** 9\
**Page:** 1

<div class="post-metadata">

**Author:** ![andrea.minu](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/andrea.minu/32/3326_2.png) [@andrea.minu](https://forum.inductiveautomation.com/u/andrea.minu)\
**Post date:** [June 14, 2017, 1:31pm UTC](https://forum.inductiveautomation.com/t/allen-bradley-1783-natr-network-address-translation-router/14515/1 "2017-06-14T13:31:00Z")

</div>

Hello  
Has anyone connected Ignition a Allen Bradley PLC ( SLC and Controllogix) using a 1783-NATR

> **[enet-pp011\_-en-p.pdf](https://literature.rockwellautomation.com/idc/groups/literature/documents/pp/enet-pp011_-en-p.pdf)**
>
> 990.57 KB

I have between Ignition and PLC the 1783-NATR, it is correctly configurated , I can ping the PLCs and I can connect to them via RSLINX, but Ignition is not able to connects.

Without the NAT 1783 , the connection works correctly.

The Pc of Ignition is 192.168.1.80 and the 1783 NAT is configurated like in the picture

 ![](https://us1.discourse-cdn.com/inductiveautomation/original/2X/9/90b421130442da7d5987b824612ea60a8941d9f1.PNG)

In the configuration of the device I used the following IP

PLC 1 = 169.254.1.46  
PLC 2= 169.254.1.47

But ignition remains In the status “Connecting”

any suggestion is appreciated

Thank you very much

Best regards

Andrea

---

<div class="post-metadata">

**Author:** ![paul-griffith](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/paul-griffith/32/37249_2.png) [@paul-griffith](https://forum.inductiveautomation.com/u/paul-griffith)\
**Post date:** [June 14, 2017, 4:12pm UTC](https://forum.inductiveautomation.com/t/allen-bradley-1783-natr-network-address-translation-router/14515/2 "2017-06-14T16:12:11Z")

</div>

Is anything being logged into the gateway console? Go to Status -\> Diagnostics -\> Logs and see if there’s anything related to the device connections you’re trying to set up.

---

<div class="post-metadata">

**Author:** ![accyroy](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/accyroy/32/3386_2.png) [@accyroy](https://forum.inductiveautomation.com/u/accyroy)\
**Post date:** [June 14, 2017, 4:53pm UTC](https://forum.inductiveautomation.com/t/allen-bradley-1783-natr-network-address-translation-router/14515/3 "2017-06-14T16:53:27Z")

</div>

We’ve got quite a few PLC’s connected through the 1783-NATR, the connection in Ignition is standard and shouldn’t be a problem if all other networking is correct. It is really important that the PLC has it’s gateway setup properly.  
You seem to have 3 networks in play here, 192.168, 169.254 and 172.20, do you have routing between them via a gateway? We usually only have two networks when working with the NATR.  
Are you pinging and connecting via RSLinx from the Ignition server itself?

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [June 14, 2017, 5:17pm UTC](https://forum.inductiveautomation.com/t/allen-bradley-1783-natr-network-address-translation-router/14515/4 "2017-06-14T17:17:10Z")

</div>

Any time you encounter an IP address of the form 169.254.x.y, you almost certainly have a misconfigured network. These addresses are reserved for automatic addressing in the absence of any DHCP or BOOTP services. See the explanation of [Link Local addresses](https://en.wikipedia.org/wiki/Link-local_address) on wikipedia. Since these addresses can be different at every boot, you must never hard-code them anywhere.

---

<div class="post-metadata">

**Author:** ![andrea.minu](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/andrea.minu/32/3326_2.png) [@andrea.minu](https://forum.inductiveautomation.com/u/andrea.minu)\
**Post date:** [June 21, 2017, 2:10pm UTC](https://forum.inductiveautomation.com/t/allen-bradley-1783-natr-network-address-translation-router/14515/5 "2017-06-21T14:10:02Z")

</div>

Hi  
I fixed!!  
The issue was a network route rules problem  
Thank you very much  
Best regards

Andrea

---

<div class="post-metadata">

**Author:** ![cmorden](https://avatars.discourse-cdn.com/v4/letter/c/ecccb3/32.png) [@cmorden](https://forum.inductiveautomation.com/u/cmorden)\
**Post date:** [June 13, 2018, 6:16pm UTC](https://forum.inductiveautomation.com/t/allen-bradley-1783-natr-network-address-translation-router/14515/6 "2018-06-13T18:16:12Z")

</div>

I’m having a similar issue. Assuming the network route rules was a setting in the NAT itself?

---

<div class="post-metadata">

**Author:** ![anthony.lacey](https://avatars.discourse-cdn.com/v4/letter/a/4491bb/32.png) [@anthony.lacey](https://forum.inductiveautomation.com/u/anthony.lacey)\
**Post date:** [July 6, 2021, 11:31am UTC](https://forum.inductiveautomation.com/t/allen-bradley-1783-natr-network-address-translation-router/14515/7 "2021-07-06T11:31:53Z")

</div>

Hi Andrea. Would you share how you connected ignition to your plc thru the NATR please?

---

<div class="post-metadata">

**Author:** ![Xander\_Castillo](https://avatars.discourse-cdn.com/v4/letter/x/dbc845/32.png) [@Xander\_Castillo](https://forum.inductiveautomation.com/u/Xander_Castillo)\
**Post date:** [February 17, 2023, 2:11pm UTC](https://forum.inductiveautomation.com/t/allen-bradley-1783-natr-network-address-translation-router/14515/8 "2023-02-17T14:11:36Z")

</div>

I cannot connect to a Micro850 via Modbus with a NAT, the status in the Device is Connecting.  
any Idea?

---

<div class="post-metadata">

**Author:** ![Alfredo\_Egmo](https://avatars.discourse-cdn.com/v4/letter/a/ccd318/32.png) [@Alfredo\_Egmo](https://forum.inductiveautomation.com/u/Alfredo_Egmo)\
**Post date:** [April 9, 2025, 2:01pm UTC](https://forum.inductiveautomation.com/t/allen-bradley-1783-natr-network-address-translation-router/14515/9 "2025-04-09T14:01:33Z")

</div>

as reference in case that anyonelse needs information, check this also:

[Connecting PLC to Ignition through 1783-NATR - Ignition - Inductive Automation Forum](https://forum.inductiveautomation.com/t/connecting-plc-to-ignition-through-1783-natr/97027/8)