How would I address a tag to look at a Micrologix 1100’s RTC minute?

I have tried

[DeviceName]RTC:0.min  
and  
[DeviceName]RTC:0.MIN

[DeviceName]S2:41 does not carry the minute in a Micrologix like a SLC does.

Is there another way I am missing? I tried the above because this is the normal AB way to address it.

Any advice?

Mike

---

<div class="post-metadata">

**Author:** ![markdobtech](https://avatars.discourse-cdn.com/v4/letter/m/71e660/32.png) [@markdobtech](https://forum.inductiveautomation.com/u/markdobtech)\
**Post date:** [October 10, 2013, 6:11pm UTC](https://forum.inductiveautomation.com/t/allen-bradley-micrologix-rtc/7396/2 "2013-10-10T18:11:09Z")

</div>

I believe in ladder you will need to copy the RTC:0.MIN to an N:x to expose it. Then refer to the N register from OPC to Sql Tag.

---

<div class="post-metadata">

**Author:** ![Robert.McKenzie](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/robert.mckenzie/32/4134_2.png) [@Robert.McKenzie](https://forum.inductiveautomation.com/u/Robert.McKenzie)\
**Post date:** [October 10, 2013, 6:15pm UTC](https://forum.inductiveautomation.com/t/allen-bradley-micrologix-rtc/7396/3 "2013-10-10T18:15:15Z")

</div>

Yeah, I’d just copy it to an N register.