# Allen Bradly Control Logix - Progress Bar updating issue

**URL:** <https://forum.inductiveautomation.com/t/allen-bradly-control-logix-progress-bar-updating-issue/63593>\
**Category:** Ignition\
**Tags:** vision, ignition81\
**Created:** [August 30, 2022, 9:14am UTC](https://forum.inductiveautomation.com/t/allen-bradly-control-logix-progress-bar-updating-issue/63593 "2022-08-30T09:14:07Z")\
**Posts on this page:** 1\
**Showing post:** 2

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [August 30, 2022, 12:11pm UTC](https://forum.inductiveautomation.com/t/allen-bradly-control-logix-progress-bar-updating-issue/63593/2 "2022-08-30T12:11:16Z")

</div>

Take a screenshot of your device's diagnostic page. It sounds like you've overloaded it. This is often caused by a newbie mistake: dragging everything from the OPC browser over to Ignition's tag browser. (You should only have tags in Ignition for the OPC items you need.)

FWIW, a 10ms scan time is overly optimistic for any polling PLC driver in Ignition.

This topic should help:

> [@Ignition & Logix Best Practice Tips for better communications](https://forum.inductiveautomation.com/t/ignition-logix-best-practice-tips-for-better-communications/60386):
>
> Hi All, After a whole bunch of issues I have gone down the rabbit hole of what is wrong with our setup on site. I will preface this by saying I a relatively new to all of this… so be gentle stuck_out_tongue Based on much reading(such wow) I believe I have a list of things our site could take away for a better system. Some of them are easy to implement, whilst some of them need… significant work to realize. Especially the AOI approach in point 5 expressionless Before going too far and up…

---

_[View the full topic](https://forum.inductiveautomation.com/t/allen-bradly-control-logix-progress-bar-updating-issue/63593)._