If a NumericEntryField is tied to an OPC tag with a bidirectional tag binding (indirect in this case), is the tag write suppose to be recorded to the audit log when a user changes the value? I am only seeing tag write changes for memory tags.

---

<div class="post-metadata">

**Author:** ![Nathan\_Foster](https://avatars.discourse-cdn.com/v4/letter/n/ecd19e/32.png) [@Nathan\_Foster](https://forum.inductiveautomation.com/u/Nathan_Foster)\
**Post date:** [April 18, 2024, 9:24pm UTC](https://forum.inductiveautomation.com/t/audit-log-not-recording-changes/88935/2 "2024-04-18T21:24:39Z")

</div>

Found the issue. The OPC tags were a red herring. The 'ORIGINATING\_SYSTEM' column was getting maxed out causing a java exception. I altered the column from nvarchar(255) to nvarchar(max) which fixed the issue.

---

<div class="post-metadata">

**Author:** ![jlandwerlen](https://avatars.discourse-cdn.com/v4/letter/j/bc8723/32.png) [@jlandwerlen](https://forum.inductiveautomation.com/u/jlandwerlen)\
**Post date:** [April 18, 2024, 11:01pm UTC](https://forum.inductiveautomation.com/t/audit-log-not-recording-changes/88935/3 "2024-04-18T23:01:27Z")

</div>

That bit me too.