# Automation Professionals' Advanced Modbus Driver

**URL:** <https://forum.inductiveautomation.com/t/automation-professionals-advanced-modbus-driver/41312>\
**Category:** 3rd Party Modules\
**Created:** [December 8, 2020, 8:45pm UTC](https://forum.inductiveautomation.com/t/automation-professionals-advanced-modbus-driver/41312 "2020-12-08T20:45:46Z")\
**Posts on this page:** 20\
**Page:** 4

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [June 6, 2024, 9:03pm UTC](https://forum.inductiveautomation.com/t/automation-professionals-advanced-modbus-driver/41312/61 "2024-06-06T21:03:47Z")

</div>

Hi Andres,

No, I have not, and have no prospects to do so. I have no access to a specification for it.

BTW, I have now replied twice to your email inquiries. You should look for them in your mail system. (A few minutes ago, and back on May 3rd. My email server says your email server **accepted** the messages.)

Phil

---

<div class="post-metadata">

**Author:** ![Andres\_Rossi](https://avatars.discourse-cdn.com/v4/letter/a/87869e/32.png) [@Andres\_Rossi](https://forum.inductiveautomation.com/u/Andres_Rossi)\
**Post date:** [June 10, 2024, 5:57pm UTC](https://forum.inductiveautomation.com/t/automation-professionals-advanced-modbus-driver/41312/62 "2024-06-10T17:57:17Z")

</div>

Thanks for the response Phil.  
Unfortunately my email system is blocking your emails and I can't see them. Would you mind resending them to [arossi.aci@gmail.com](mailto:arossi.aci@gmail.com)?

Thanks in advance.  
Regards, Andres

---

<div class="post-metadata">

**Author:** ![SHuidrom](https://avatars.discourse-cdn.com/v4/letter/s/3be4f8/32.png) [@SHuidrom](https://forum.inductiveautomation.com/u/SHuidrom)\
**Post date:** [August 23, 2024, 2:35am UTC](https://forum.inductiveautomation.com/t/automation-professionals-advanced-modbus-driver/41312/63 "2024-08-23T02:35:38Z")

</div>

@pturmel , while testing this advanced modbus driver configured as an advanced client connected with redundant slave devices. The problem is when i disconnect both the redundant devices the driver status on the device connection shows "Connected" and the status remains "Connected" until figured out.

In the second test, If one link is up out of the redundant client devices, it shows "Connected Recovering", and if i disconnect the live single link, the status remains "Connected Recovering", which is not an ideal scenario.  
Is there a fix for this one ? thanks.

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [August 23, 2024, 11:59am UTC](https://forum.inductiveautomation.com/t/automation-professionals-advanced-modbus-driver/41312/64 "2024-08-23T11:59:40Z")

</div>

Thanks for the report. Will investigate.

---

<div class="post-metadata">

**Author:** ![Kamil\_Muza](https://avatars.discourse-cdn.com/v4/letter/k/cab0a1/32.png) [@Kamil\_Muza](https://forum.inductiveautomation.com/u/Kamil_Muza)\
**Post date:** [September 13, 2024, 8:22pm UTC](https://forum.inductiveautomation.com/t/automation-professionals-advanced-modbus-driver/41312/65 "2024-09-13T20:22:18Z")

</div>

Does Automation Professional's Modbus driver allows for multiple Modbus TCP servers/slaves on different tcp ports simultaneously?

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [September 13, 2024, 8:23pm UTC](https://forum.inductiveautomation.com/t/automation-professionals-advanced-modbus-driver/41312/66 "2024-09-13T20:23:16Z")

</div>

Yes. Multiple server instances are supported. A single instance can also listen on multiple ports.

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [September 23, 2024, 6:02pm UTC](https://forum.inductiveautomation.com/t/automation-professionals-advanced-modbus-driver/41312/67 "2024-09-23T18:02:13Z")

</div>

Automation Professionals is pleased to announce that this Advanced Modbus driver is now available for purchase for Ignition Edge, with a steep discount. See Automation Professionals' updated Module Sales Policy here:

[https://www.automation-pros.com/Module%20Sales-2024-11-05.pdf](https://www.automation-pros.com/Module%20Sales-2024-11-05.pdf)

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [September 26, 2024, 6:26pm UTC](https://forum.inductiveautomation.com/t/automation-professionals-advanced-modbus-driver/41312/68 "2024-09-26T18:26:24Z")

</div>

Automation Professionals is pleased to announce a new production release of the Advanced Modbus Module.

For Ignition v8.1.x: ~~v1.1.7.242701819~~

This includes a bugfix for the driver status problem mentioned in [comment #63](https://forum.inductiveautomation.com/t/automation-professionals-advanced-modbus-driver/41312/63) above.

This includes the constrained Transaction ID feature requested in this topic:

> [@Modbus TCP - Moore / Siemens 353](https://forum.inductiveautomation.com/t/modbus-tcp-moore-siemens-353/95970):
>
> I have a new installation with a Moore / Siemens 353 controller using Modbus TCP. It all works great for the first 15 or so minutes - then, it just times-out and cycles from connecting/disconnecting/etc. If I disable/enable, it starts to work again - for 15 minutes. Is there some obvious setting that I can change to correct this behavior?

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [October 1, 2024, 2:55pm UTC](https://forum.inductiveautomation.com/t/automation-professionals-advanced-modbus-driver/41312/69 "2024-10-01T14:55:37Z")

</div>

Automation Professionals is pleased to announce a new production release of the Advanced Modbus Module.

For Ignition v8.1.x: ~~v1.1.8.242731956~~

This release fixes a client driver bug in holding register Masked Write operations, as reported by @woodsb02 over here, long ago:

> [@Ignition OPC UA Server Redundancy (Modbus TCP)](https://forum.inductiveautomation.com/t/ignition-opc-ua-server-redundancy-modbus-tcp/67123/13):
>
> Actually, I think I may have found a bug when used with [bit-level addressing and Modbus mask-write](https://docs.inductiveautomation.com/display/DOC81/Modbus+Addressing#ModbusAddressing-Bit-LevelAddressing). Not sure if its new with this redundant BETA version or pre-existing. My test setup (both the modbus server and client are using your advanced modbus driver): Modbus Server listening on 0.0.0.0 Modbus Advanced Client connecting to 127.0.0.1 and 127.0.0.2 Setup a boolean OPC tag which uses the Modbus advanced client device. Using this address works: ns=1;s=[client]1.C1 Using this address work…

I couldn't reproduce with the designer tag browser or with fire-and-forget writes, because the actual write worked. The breakthrough came when I scripted my testing with `system.opc.writeValue()`. _Boom!_

This bug goes all the way back to the beta. All users should upgrade.

_Sigh._

---

<div class="post-metadata">

**Author:** ![woodsb02](https://avatars.discourse-cdn.com/v4/letter/w/6a8cbe/32.png) [@woodsb02](https://forum.inductiveautomation.com/u/woodsb02)\
**Post date:** [October 7, 2024, 9:36am UTC](https://forum.inductiveautomation.com/t/automation-professionals-advanced-modbus-driver/41312/70 "2024-10-07T09:36:15Z")

</div>

Hi @pturmel, can I please ask how your driver behaves on the non-active backup server configured in warm mode?

In the manual it says “only the active server will open the given ports” - does this mean it ignores the “warm mode” setting?

Does this change when an alternate target/port is configured for modbus redundancy?

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [October 7, 2024, 11:38am UTC](https://forum.inductiveautomation.com/t/automation-professionals-advanced-modbus-driver/41312/71 "2024-10-07T11:38:30Z")

</div>

> [@woodsb02](#):
>
> does this mean it ignores the “warm mode” setting?

Yes, this. My drivers are always cold.

---

<div class="post-metadata">

**Author:** ![woodsb02](https://avatars.discourse-cdn.com/v4/letter/w/6a8cbe/32.png) [@woodsb02](https://forum.inductiveautomation.com/u/woodsb02)\
**Post date:** [October 7, 2024, 11:39am UTC](https://forum.inductiveautomation.com/t/automation-professionals-advanced-modbus-driver/41312/72 "2024-10-07T11:39:42Z")

</div>

Ok, thanks for confirming 🥶

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [October 8, 2024, 2:45pm UTC](https://forum.inductiveautomation.com/t/automation-professionals-advanced-modbus-driver/41312/73 "2024-10-08T14:45:36Z")

</div>

Automation Professionals is pleased to announce a new production release of this driver:

For Ignition v8.1+: ~~v1.1.9.242811552~~

This provides a better fix for the device connection status information, and fixes a potential bug in the Modbus TCP transaction ID limit feature recently introduced.

---

<div class="post-metadata">

**Author:** ![Andres\_Rossi](https://avatars.discourse-cdn.com/v4/letter/a/87869e/32.png) [@Andres\_Rossi](https://forum.inductiveautomation.com/u/Andres_Rossi)\
**Post date:** [October 22, 2024, 2:39pm UTC](https://forum.inductiveautomation.com/t/automation-professionals-advanced-modbus-driver/41312/74 "2024-10-22T14:39:03Z")

</div>

Hi Phil,  
Sorry if someone already asked this,  
Does the driver have any practical limitations regarding the maximum number of devices that can be connected? Or regarding the maximum number of TAGs between all devices? Or regarding the number of updates/sec that it can process?

In my case I have around +2500 Modbus TCP devices and +2000 Modbus RTU over TCP with an average of 200 TAGs each at a scan rate of 1min (only 20% of the TAGs change in each scan) and I want to have an idea of ​​the size or amount of I/O gateways I need.

Thanks!

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [October 22, 2024, 2:48pm UTC](https://forum.inductiveautomation.com/t/automation-professionals-advanced-modbus-driver/41312/75 "2024-10-22T14:48:17Z")

</div>

I don't have any users with such an extreme workload, but I would expect it to be possible with enough CPU cores and RAM. There's no hard-coded limits in the software.

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [November 8, 2024, 9:50pm UTC](https://forum.inductiveautomation.com/t/automation-professionals-advanced-modbus-driver/41312/76 "2024-11-08T21:50:50Z")

</div>

Automation Professionals is pleased to announce a BETA release of this Advanced Modbus driver module, with one bugfix and two features.

For Ignition v8.1+: ~~v1.1.10.243132114~~

- Fixed a bug in diagnostics that breaks device diagnostics for **all** devices in the gateway--that page then looks like no devices are configured. Due to `RateStats` losing its `Comparable<>` interface somewhere along the way. (And me not noticing.)

- Added `[Diagnostics]` folder to OPC browsing--basically a port of the code from the EtherNet/IP driver's `Driver` implementation. While in that mess, added separate diagnostic booleans for `ConnectedA` and `ConnectedB` when using live redundant connections.

- Altered the OPC browse to fan out the tree of OPC Item Paths in smaller increments, to dramatically reduce the amount of scrolling needed to browse to specific points.

The bugfix has been cooking for a couple weeks, so that is solid, but the new diagnostics are only lightly tested, and the new OPC fanout is _barely_ tested.

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [January 7, 2025, 5:17pm UTC](https://forum.inductiveautomation.com/t/automation-professionals-advanced-modbus-driver/41312/77 "2025-01-07T17:17:32Z")

</div>

Automation Professionals is pleased to announce a new **production** release of this module, with a number of bugfixes, and the new support for scripted device creation (as mentioned [over here](https://forum.inductiveautomation.com/t/advanced-modbus-module-scripting-device-creation/98714/3)):

For Ignition v8.1+: ~~v1.1.11.250071612~~

Notable fixes:

- File Register read/write framing errors for RTU connections.
- Input/Holding/File Register corrupted word swapping for all 64-bit data types.
- Missing parser entry for the "IBCD" data transform for IR, HR, and HR addresses.
- Fixed stray errors (NPEs in particular) on device shutdown.
- Fixed Server failure to recover from RTU over TCP channel failures by applying idle TCP timeout to them.

This version also includes BETA support for Extended Lufkin Address Mode ("ELAM"), which expands the range of unit addresses to 0-2295. This support is **only** in the client driver. The client driver does **not** use this protocol extension's large packet functionality.

Corresponding support for the Server driver type, excluding large packet functionality, is planned. (If only for my own QA purposes.)

All users should upgrade.

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [January 13, 2025, 10:02pm UTC](https://forum.inductiveautomation.com/t/automation-professionals-advanced-modbus-driver/41312/78 "2025-01-13T22:02:48Z")

</div>

Automation Professionals is pleased to announce a new **production** release of this module, with one more RTU bugfix and an implementation of Schneider's "Mod10" totalizer data format.

For Ignition v8.1+: ~~v1.1.12.250132149~~

The Lufkin ELAM support is still a BETA.

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [January 28, 2025, 11:17pm UTC](https://forum.inductiveautomation.com/t/automation-professionals-advanced-modbus-driver/41312/79 "2025-01-28T23:17:08Z")

</div>

Automation Professionals is pleased to announce a new **BETA** release of this module. It ~~is functionally identical to v1.1.12, but~~ has been completely refactored to run through the `Device` interface instead of the `Driver` interface. The only functional change is a switch to `SamplingMetrics` instead of `PollingMetrics`. That moves the minimum supported platform version to 8.1.7.

I **think** I've wrapped my head around this monster, and I can see the many functional opportunities this enables. But it just--_ **finally** _--passed my internal QA this afternoon. 😬

This conversion is a blocker for v8.3 support, so I've been cracking my skull to get this done. Feedback is greatly appreciated.

For Ignition v8.1+: ~~v1.1.13.250282248~~

{FWIW, I _implemented_ `Device`. I did **not** _extend_ `ManagedDevice`.}

For the extra curious:

```python
git diff --stat 5fd6ecd250ed67..d9198670b521 Gateway/src
 Gateway/src/com/automation_pros/modbus/DeviceGwHook.java | 113 ++++++
 Gateway/src/com/automation_pros/modbus/address/ModbusAddress.java | 27 +-
 Gateway/src/com/automation_pros/modbus/address/ModbusBitAddress.java | 324 ++++++++--------
 Gateway/src/com/automation_pros/modbus/address/ModbusFieldAddress.java | 219 +++++------
 Gateway/src/com/automation_pros/modbus/address/ModbusNumericAddress.java | 48 +--
 Gateway/src/com/automation_pros/modbus/address/ModbusStringAddress.java | 260 ++++++-------
 Gateway/src/com/automation_pros/modbus/client/AbstractClientReadReq.java | 178 +++++----
 Gateway/src/com/automation_pros/modbus/client/AbstractClientReq.java | 2 +-
 Gateway/src/com/automation_pros/modbus/client/AbstractClientWriteReq.java | 158 ++++----
 Gateway/src/com/automation_pros/modbus/client/ReadBitsReq.java | 3 +-
 Gateway/src/com/automation_pros/modbus/client/ReadFileReq.java | 9 +-
 Gateway/src/com/automation_pros/modbus/client/ReadRegsReq.java | 3 +-
 Gateway/src/com/automation_pros/modbus/client/WriteCoilReq.java | 163 ++++----
 Gateway/src/com/automation_pros/modbus/client/WriteCoilsReq.java | 187 +++++----
 Gateway/src/com/automation_pros/modbus/client/WriteFileReq.java | 31 +-
 Gateway/src/com/automation_pros/modbus/client/WriteMaskedReq.java | 180 +++++----
 Gateway/src/com/automation_pros/modbus/client/WriteRegReq.java | 170 ++++-----
 Gateway/src/com/automation_pros/modbus/client/WriteRegsReq.java | 196 +++++-----
 Gateway/src/com/automation_pros/modbus/config/DeviceConfigAction.java | 80 ++++
 Gateway/src/com/automation_pros/modbus/config/ModbusClientDeviceType.java | 51 +++
 Gateway/src/com/automation_pros/modbus/config/ModbusClientDriverType.java | 33 +-
 Gateway/src/com/automation_pros/modbus/config/ModbusConfigLink.java | 31 ++
 Gateway/src/com/automation_pros/modbus/config/ModbusServerDeviceType.java | 51 +++
 Gateway/src/com/automation_pros/modbus/config/ModbusServerDriverType.java | 88 ++---
 Gateway/src/com/automation_pros/modbus/config/settings/AbstractModbusSettings.java | 4 +-
 Gateway/src/com/automation_pros/modbus/config/web/ModbusDriverSummary.java | 145 ++++---
 Gateway/src/com/automation_pros/modbus/config/web/ModbusUnitEdit.java | 3 +-
 Gateway/src/com/automation_pros/modbus/config/web/ModbusUnitsConfig.java | 560 ++++++++++++++-------------
 Gateway/src/com/automation_pros/modbus/driver/GenericBase.java | 1410 +++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++++
 Gateway/src/com/automation_pros/modbus/driver/GenericDevice.java | 599 +++++++++++++++++++++++++++++
 Gateway/src/com/automation_pros/modbus/driver/GenericDriver.java | 1485 ++++++-----------------------------------------------------------------
 Gateway/src/com/automation_pros/modbus/driver/GenericModbusDriver.java | 63 ++-
 Gateway/src/com/automation_pros/modbus/driver/ModbusClient.java | 75 ++--
 Gateway/src/com/automation_pros/modbus/driver/ModbusServer.java | 698 ++++++++++++++++-----------------
 Gateway/src/com/automation_pros/modbus/driver/RedundancyHandler.java | 391 +++++++++----------
 Gateway/src/com/automation_pros/modbus/handlers/DoubleHandler.java | 150 ++++----
 Gateway/src/com/automation_pros/modbus/handlers/FloatHandler.java | 94 ++---
 Gateway/src/com/automation_pros/modbus/handlers/IntBcdHandler.java | 94 ++---
 Gateway/src/com/automation_pros/modbus/handlers/IntHandler.java | 92 ++---
 Gateway/src/com/automation_pros/modbus/handlers/LongHandler.java | 150 ++++----
 Gateway/src/com/automation_pros/modbus/handlers/Mod10Handler.java | 14 +-
 Gateway/src/com/automation_pros/modbus/handlers/ModbusHandler.java | 68 ++--
 Gateway/src/com/automation_pros/modbus/handlers/ModbusOpcHandler.java | 66 ++--
 Gateway/src/com/automation_pros/modbus/handlers/ShortBcdHandler.java | 58 +--
 Gateway/src/com/automation_pros/modbus/handlers/ShortHandler.java | 58 +--
 Gateway/src/com/automation_pros/modbus/server/MaskWriteRegCmd.java | 89 ++---
 Gateway/src/com/automation_pros/modbus/server/ReadBitsCmd.java | 17 +-
 Gateway/src/com/automation_pros/modbus/server/ReadFileCmd.java | 201 +++++-----
 Gateway/src/com/automation_pros/modbus/server/ReadRegsCmd.java | 121 +++---
 Gateway/src/com/automation_pros/modbus/server/WriteCoilCmd.java | 113 +++---
 Gateway/src/com/automation_pros/modbus/server/WriteCoilsCmd.java | 11 +-
 Gateway/src/com/automation_pros/modbus/server/WriteFileCmd.java | 201 +++++-----
 Gateway/src/com/automation_pros/modbus/server/WriteReadRegsCmd.java | 127 +++---
 Gateway/src/com/automation_pros/modbus/server/WriteRegCmd.java | 89 ++---
 Gateway/src/com/automation_pros/modbus/server/WriteRegsCmd.java | 113 +++---
 55 files changed, 5507 insertions(+), 4457 deletions(-)

```

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [January 29, 2025, 10:14pm UTC](https://forum.inductiveautomation.com/t/automation-professionals-advanced-modbus-driver/41312/80 "2025-01-29T22:14:01Z")

</div>

Another BETA. Fixed sampling stats, as well as possible.

For Ignition v8.1+: ~~v1.1.13.250292153~~

With the standard Device Status graphics, I cannot make "Actual Sampling Interval" show up properly. That display adds the Queue Duration to the desired Sampling Interval, assuming that queue timing adds to the sampling time.

But that isn't true in my driver architecture. At the start of each poll interval for a given pace, my architecture generates optimized requests for **all** monitored items at that pace and _ **queues them** _. Which means there is always some time in queue, averaging a little less than the actual time needed to get all the responses.

So, to get actual sampling time with my driver, ignore the Device Status page, and get it from the OPC diagnostic item for that pace.

Also note that I deliver a proper overload percentage that accurately reflects the relationship between the actual sampling interval and the desired sampling interval. When overload is zero, that pace is just keeping up.

Unlike IA's driver, I report a negative overload when there is spare bandwidth.

[Previous page](https://forum.inductiveautomation.com/t/automation-professionals-advanced-modbus-driver/41312.md?page=3)

[Next page](https://forum.inductiveautomation.com/t/automation-professionals-advanced-modbus-driver/41312.md?page=5)