# Automation Professionals' EtherNet/IP Communication Suite V2

**URL:** <https://forum.inductiveautomation.com/t/automation-professionals-ethernet-ip-communication-suite-v2/68190>\
**Category:** 3rd Party Modules\
**Tags:** ignition81\
**Created:** [January 3, 2023, 10:16pm UTC](https://forum.inductiveautomation.com/t/automation-professionals-ethernet-ip-communication-suite-v2/68190 "2023-01-03T22:16:54Z")\
**Posts on this page:** 20\
**Page:** 10

<div class="post-metadata">

**Author:** ![amarks](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/amarks/32/45610_2.png) [@amarks](https://forum.inductiveautomation.com/u/amarks)\
**Post date:** [April 4, 2025, 5:52pm UTC](https://forum.inductiveautomation.com/t/automation-professionals-ethernet-ip-communication-suite-v2/68190/183 "2025-04-04T17:52:03Z")

</div>

Phil,

How does this driver treat Alias tags? They seem to be missing from the configuration when I import my L5X. (how do other drivers treat them - for that matter?)

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [April 4, 2025, 5:56pm UTC](https://forum.inductiveautomation.com/t/automation-professionals-ethernet-ip-communication-suite-v2/68190/184 "2025-04-04T17:56:52Z")

</div>

My host driver discards them on import. I theoretically could support them there, but haven't taken the time to implement that.

My client driver treats them like independent tags because the processor browse protocol has some ambiguity about them. (Same as IA's driver.)

You should never target alias tags from Ignition, as they are totally unoptimizable. Like, will crush your connection performance. Which makes me want to **not** implement this in the Host Device type.

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [May 27, 2025, 4:01pm UTC](https://forum.inductiveautomation.com/t/automation-professionals-ethernet-ip-communication-suite-v2/68190/185 "2025-05-27T16:01:25Z")

</div>

Automation Professionals is pleased to release a new **BETA** of this driver, with some bug fixes from the last beta, plus a bug fix for Logix "DT" aka "UTIME" data type support.

For Ignition v8.1.7+: ~~v2.1.20.251471538~~

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [June 3, 2025, 2:50pm UTC](https://forum.inductiveautomation.com/t/automation-professionals-ethernet-ip-communication-suite-v2/68190/186 "2025-06-03T14:50:12Z")

</div>

More bugfixes. Still BETA.

For Ignition v8.1.7+: ~~v2.1.20.251532105~~

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [September 29, 2025, 8:44pm UTC](https://forum.inductiveautomation.com/t/automation-professionals-ethernet-ip-communication-suite-v2/68190/187 "2025-09-29T20:44:28Z")

</div>

More bugfixes last week. Still BETA, but feeling pretty good about this one:

For Ignition v8.1.8+: [v2.1.20.252681756](https://www.automation-pros.com/ignition/EthernetIP%20Class%201%20Communications-2.1.20.252681756-v81.modl)

(Will be renumbered to v2.2.0 upon release--I've been cherry-picking back and forth with the v8.3 branch and these are very close to functionally identical.)

---

<div class="post-metadata">

**Author:** ![Aaron\_Shivnen](https://avatars.discourse-cdn.com/v4/letter/a/c2a13f/32.png) [@Aaron\_Shivnen](https://forum.inductiveautomation.com/u/Aaron_Shivnen)\
**Post date:** [September 30, 2025, 7:49pm UTC](https://forum.inductiveautomation.com/t/automation-professionals-ethernet-ip-communication-suite-v2/68190/188 "2025-09-30T19:49:55Z")

</div>

@pturmel in another topic about sticking momentary buttons you mentioned your improved Logix Driver. Is this that driver? Will it help make momentary buttons more reliable?

I agree, that they should be avoided but I am not the one making the call to keep the buttons in place. We use our momentary buttons to jog a conveyor/s if needed.

Appreciate a response, thank you.

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [September 30, 2025, 8:12pm UTC](https://forum.inductiveautomation.com/t/automation-professionals-ethernet-ip-communication-suite-v2/68190/189 "2025-09-30T20:12:20Z")

</div>

> [@Aaron\_Shivnen](#):
>
> Will it help make momentary buttons more reliable?

This driver module includes a high-reliability momentary button for **Vision** , which only works with the module's Class1 I/O buffers (Scanner or Adapter modes). It does not work with the Generic EtherNet/IP Client driver type, nor with any other driver.

---

<div class="post-metadata">

**Author:** ![vbosmiya](https://avatars.discourse-cdn.com/v4/letter/v/7993a0/32.png) [@vbosmiya](https://forum.inductiveautomation.com/u/vbosmiya)\
**Post date:** [November 13, 2025, 7:04pm UTC](https://forum.inductiveautomation.com/t/automation-professionals-ethernet-ip-communication-suite-v2/68190/190 "2025-11-13T19:04:43Z")

</div>

We are trying to connect to cygnus commkit using **EthernetIP Class 1 Communications module in Ignition and having a hard time to make it work. Here is the commkit instructions manual.** [https://www.maxcessintl.com/wp-content/uploads/2022/05/MAGPOWR-COMMKIT-Fieldbus-Interface-Cards-Instruction-Manual.pdf](https://www.maxcessintl.com/wp-content/uploads/2022/05/MAGPOWR-COMMKIT-Fieldbus-Interface-Cards-Instruction-Manual.pdf)

Before we buy the Ethernet Module, we need to make sure it works. Can you please advise on this ?

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [November 13, 2025, 7:34pm UTC](https://forum.inductiveautomation.com/t/automation-professionals-ethernet-ip-communication-suite-v2/68190/191 "2025-11-13T19:34:13Z")

</div>

Please provide a link to the nested HMS AnyBus model. The manual say 4173, but that doesn't show up on the HMS website. Or provide the PDF manual and EIP EDS file (not the DNet EDS).

Generally, AnyBus EtherNet/IP products work exactly as expected, but provide **zero** data conversion or byte ordering.

This Maxcess product is big endian, while EIP is little endian. This will be a challenge.

The Maxcess manual suggests that you should be able to use GetAttributeSingle messages, but provides no details of class, instance, and attribute numbers. This will be a challenge.

You haven't provided enough information to determine if scanner mode would work.

The poor quality of the documentation makes me hesitant to endorse this product with my driver.

---

<div class="post-metadata">

**Author:** ![vbosmiya](https://avatars.discourse-cdn.com/v4/letter/v/7993a0/32.png) [@vbosmiya](https://forum.inductiveautomation.com/u/vbosmiya)\
**Post date:** [November 13, 2025, 8:07pm UTC](https://forum.inductiveautomation.com/t/automation-professionals-ethernet-ip-communication-suite-v2/68190/192 "2025-11-13T20:07:52Z")

</div>

Here is the commkit module that we have plugged in to the Cygnus Controller.

[https://www.maxcessintl.com/wp-content/uploads/2022/05/MAGPOWR-COMMKIT-Fieldbus-Interface-Cards-Instruction-Manual.pdf](https://www.maxcessintl.com/wp-content/uploads/2022/05/MAGPOWR-COMMKIT-Fieldbus-Interface-Cards-Instruction-Manual.pdf)

This is some of the information that I have received from Maxaccess who sold us the commkit unit. Also I did some digging and saw how I can make it work with Ignition and that's how I landed up with your module as its ethernet based. It was talking about EDS which I found from HMS website but that's just a generic version I believe and I tried that and it does not work. I got a response from HMS who asked us to reach out to Maxaccess to send the the correct EDS. See the copy of that email below.

Sorry I am sending you a lot of info here but that's the only way to figure out how we can make it work. Our end goal is to connect the commkit device to Ignition so we can record the tension data.

**Kevin Annis** (HMS-Support)

Nov 13, 2025, 17:37 GMT+1

**Hello Aniket,**

**You will need to reach out to Cygnus for the EDS file that they developed for their Commkit. The EDS we provide for the AB4173 is a template EDS file for developers to configure alongside the development of the embedded unit for their machines. Cygnus will have correct EDS file that has all the parameter and connection information need for your Ethernet/IP Scanner.**

**I do apologize for the inconvenience.**

**-Kevin**

**Email from Maxaccess**

Hi Vipul,

Good question — you do **not** need to purchase a separate external Anybus adapter.

Your **Commkit module** (the small circuit card already installed inside the Cygnus) _is itself_ an **HMS Anybus-S Ethernet/IP interface**. That’s the device that allows the Cygnus to communicate with your PLC or data collection system over Ethernet/IP.

Here’s how it works:

**How the Commkit is structured**

- The **Commkit** is a plug-in daughter card inside the Cygnus controller.
- It uses an **HMS Anybus-S chip** for the Ethernet/IP protocol.
- When you connect your Ethernet cable to the Cygnus and open the web page (like the one you showed), you’re already communicating directly with that built-in Anybus interface — no additional hardware is needed.

So the fact that you can reach the web page means your Anybus interface is active and ready to be configured.

NEXT STEPS

To get communication with your PLC or data system:

1. Use **RSLogix 5000 / Studio 5000** to add the Cygnus as a **Generic Ethernet Module** (no special EDS file required).

- Set **Comm Format** = Data - SINT
- **Input Assembly** = 100 (16 bytes)
- **Output Assembly** = 150 (16 bytes)
- **Configuration** = 1 (size 0)
- **RPI** ≈ 50 ms1. Use the **Commkit Setup** document to interpret the 16 input and 16 output bytes into meaningful data words:
- Word 0 = Message ID
- Word 1 = Parameter ID
- Word 2 = Read/Write Control
- Words 3–7 = Data fields (unsigned, integer, or float)1. Once that’s done, your PLC can start reading and writing Cygnus parameters directly.

**Summary**

- The **Commkit you already have** is the Anybus interface — no external adapter required.
- The **Ethernet port on the Cygnus** connects directly to your PLC network.
- Use the attached **RSLogix** and **Commkit setup** guides to finish the configuration.

**What Data You Can Read from the Cygnus**

The Cygnus communicates all of its internal setup and operating parameters over Ethernet/IP using the built-in **Anybus-S Commkit card**.  
Each parameter in the controller (like Tension, Diameter, Mode, Setpoint, etc.) is assigned a **Parameter ID**. Through the network, you can read or write any of these parameters.

Typical parameters you can read include:

- **Current Tension** (actual web tension value)
- **Tension Setpoint**
- **Web Width / Wrap Angle**
- **Roll Diameter** (measured or calculated)
- **Line Speed** or **Velocity**
- **System Mode** (Auto / Manual / Hold / Stopped)
- **Load Cell readings and calibration status**
- **Alarm or status codes (0xD001–0xD023)** showing operating or error conditions
- **Active Setup Number** , **Gain Scheduling** , and **Remote Inputs** configuration flags

All these values can be queried using the Ethernet/IP connection without needing to be at the front panel.

**How the Data Exchange Works**

The Commkit uses a **16-byte Input / 16-byte Output data image** , organized into 8 words of 2 bytes each:

> **Word**  
>   
> |   
>   
> **Field**  
>   
> |   
>   
> **Description**  
>   
> |
> 
> - | - | - |  
>   
>   
> 0  
>   
> |   
>   
> Message ID  
>   
> |   
>   
> Command counter (changes each new message)  
>   
> |  
>   
>   
> 1  
>   
> |   
>   
> Parameter ID  
>   
> |   
>   
> The Cygnus parameter number to read/write  
>   
> |  
>   
>   
> 2  
>   
> |   
>   
> Read/Write Control  
>   
> |   
>   
> 0 = Read, 1 = Write  
>   
> |  
>   
>   
> 3  
>   
> |   
>   
> Data (UINT)  
>   
> |   
>   
> 16-bit unsigned value  
>   
> |  
>   
>   
> 4–5  
>   
> |   
>   
> Data (INT)  
>   
> |   
>   
> 32-bit signed value  
>   
> |  
>   
>   
> 6–7  
>   
> |   
>   
> Data (FLOAT)  
>   
> |   
>   
> 32-bit IEEE floating-point value  
>   
>   
>   
> Commkit setup  
>   
> |

When you send a **read** command, the Cygnus returns the requested parameter’s value in the correct data field (UINT/INT/FLOAT).  
When you send a **write** command, the Cygnus acknowledges success by returning **Parameter ID = 0xFFFF**

**Example – Reading Actual Tension**

1. PLC sends:

- Message ID = 1
- Parameter ID = 47 (for example, Roll Width or Tension)
- Read/Write = 0 (Read)1. Cygnus responds:
- Same Message ID = 1
- Parameter ID = 47 (no error)
- Read/Write = 1
- Data field contains the **actual tension value** in FLOAT format

850A299 Commkit-EN Manual

If there’s an issue, the **Parameter ID field** will instead contain an **error code** like 0xD001–0xD023, which you can reference in the manual’s error list.

**In Summary**

Once connected via Ethernet/IP:

- You can read **real-time process data** (tension, speed, diameter, status, etc.).
- You can **write setup parameters** or **change modes remotely**.
- You can **monitor faults and system state** for diagnostics.
- Communication updates occur every 50 ms or faster, depending on your RPI setting.

This makes the Commkit a full remote interface for automation, data collection, or SCADA integration — no extra Anybus hardware or local HMI is required.

Tirrell Pullen  
Technical Support Representative  
Maxcess - Oklahoma City  
Main: 405-755-1600  
Office: 405-752-7885  
Fax: 405-724-5085

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [November 13, 2025, 8:27pm UTC](https://forum.inductiveautomation.com/t/automation-professionals-ethernet-ip-communication-suite-v2/68190/193 "2025-11-13T20:27:07Z")

</div>

(In the future, please send such data dumps to my sales or support emails.)

Ok. The EtherNet/IP part is simple. In my Host Device driver type, create two array tags of type `INT[8]` for input and output buffers. (Follow the user manual instructions for the various settings of the devices. The Local Address setting will likely need to be in the same subnet as the tension device.)

Create a scanner module within the driver with route path `port 2 your.maxcess.ip.address` and application path `assy 1 cxpt 150 cxpt 100`.

Put your tag names into the input an output settings, and choose 50000 microseconds for the RPIs.

You will have to write gateway timer scripts to cycle message IDs and parameter numbers to multiplex the data through this interface. That is beyond the scope of my pre-sales support.

---

<div class="post-metadata">

**Author:** ![karl.fjortoft](https://avatars.discourse-cdn.com/v4/letter/k/8491ac/32.png) [@karl.fjortoft](https://forum.inductiveautomation.com/u/karl.fjortoft)\
**Post date:** [December 5, 2025, 1:43pm UTC](https://forum.inductiveautomation.com/t/automation-professionals-ethernet-ip-communication-suite-v2/68190/194 "2025-12-05T13:43:40Z")

</div>

I’m pretty new to Ignition and Omron, I’m currently testing some different communication protocols as we want to try some alternatives to Kepware possibly, found this module and just been testing a bit today, works pretty good as far as I can tell.

I just have some issue with tags from structs im the Omron PLC (NJ and NX PLS’s) imported into Ignition, they get a space and struct name added to the name, this messes up with our current templates which just has the tagname and undertags, any possibility to not add the struct name?

 ![bilde](https://us1.discourse-cdn.com/inductiveautomation/original/3X/7/e/7ec6a3d57be0089bea865ab0c3cd61c14da46b96.png)

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [December 5, 2025, 2:02pm UTC](https://forum.inductiveautomation.com/t/automation-professionals-ethernet-ip-communication-suite-v2/68190/195 "2025-12-05T14:02:57Z")

</div>

> [@karl.fjortoft](#):
>
> they get a space and struct name added to the name

Only when dragging and dropping. That struct name serves two purposes:

- It cues what data type to expect from that folder, cueing the use of the corresponding auto-generated Ignition UDT under `_types_/ENIP/device/`. (Get the JSON for those from the device's configuration page.)

- It **discourages** users from dragging and dropping whole folders from the PLC, which is a newbie mistake that usually triggers horrible driver performance. Limit drag and drop to just atomic values.

The struct name is **not** part of the OPC Item Path.

I will not be changing this **deliberate** driver behavior.

When you want a whole folder from OPC, right click that node and copy the path. Then, in the Tag browser, create a new UDT instance of the displayed type, and set its `opc_something` parameter to that copied item path.

If you don't like anything about the auto-generated UDTs, you are welcome to copy into a new folder in your tag provider and tweak to your heart's content.

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [December 16, 2025, 9:50pm UTC](https://forum.inductiveautomation.com/t/automation-professionals-ethernet-ip-communication-suite-v2/68190/196 "2025-12-16T21:50:07Z")

</div>

Automation Professionals is pleased to announce a **Release Candidate** for Ignition v8.3, with updated documentation.

For Ignition v8.3: ~~v2.2.0.253501828~~

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [January 7, 2026, 9:52pm UTC](https://forum.inductiveautomation.com/t/automation-professionals-ethernet-ip-communication-suite-v2/68190/197 "2026-01-07T21:52:50Z")

</div>

Automation Professionals is pleased to announce the Production release of this driver module for Ignition v8.3. This release fixes two bugs in the release candidate above:

- A broken redundancy synchronization implementation, with broken Protobuf encodings.

- A reconnect bug when status shows "Disconnected Duplicate FwdOpen".

For Ignition v8.3: ~~v2.2.1.260072007~~

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [January 9, 2026, 8:16pm UTC](https://forum.inductiveautomation.com/t/automation-professionals-ethernet-ip-communication-suite-v2/68190/198 "2026-01-09T20:16:11Z")

</div>

Better bugfix for the duplicate FwdOpen reconnection bug. I have an L81 in my lab that doesn't appear to allow recycling connection triads as expected. ☹

For Ignition v8.3: ~~v2.2.1.260091944~~

---

<div class="post-metadata">

**Author:** ![karl.fjortoft](https://avatars.discourse-cdn.com/v4/letter/k/8491ac/32.png) [@karl.fjortoft](https://forum.inductiveautomation.com/u/karl.fjortoft)\
**Post date:** [February 27, 2026, 2:55pm UTC](https://forum.inductiveautomation.com/t/automation-professionals-ethernet-ip-communication-suite-v2/68190/199 "2026-02-27T14:55:14Z")

</div>

Thanks for helping with my previous issue, have worked it out, I had to update some of the UDT’s etc, but got it working well now.

I’m just wondering about the statistics in Ignition 8.3.3, I cannot find the “View details” in Connections-Devices-Connections like I can for the native Omron NJ driver for instance. I can see that others have posted pictures of those stats before in the thread, but that was probably for a previous version of Ignition, so maybe its changed? Thanks.

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [February 27, 2026, 3:22pm UTC](https://forum.inductiveautomation.com/t/automation-professionals-ethernet-ip-communication-suite-v2/68190/200 "2026-02-27T15:22:47Z")

</div>

It changed, and I haven't altered my implementation (yet) to show graphic diagnostics in v8.3.

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [March 17, 2026, 5:52pm UTC](https://forum.inductiveautomation.com/t/automation-professionals-ethernet-ip-communication-suite-v2/68190/201 "2026-03-17T17:52:23Z")

</div>

Automation Professionals is pleased to announce a Release Candidate for this module in v8.1. It includes backports of the latest v8.3 bug fixes and uses the `Device` model to facilitate future backports.

For Ignition v8.1.x: [v2.1.20.260761438](https://www.automation-pros.com/ignition/EthernetIP%20Class%201%20Communications-2.1.20.260761438-v81.modl)

---

<div class="post-metadata">

**Author:** ![konstantinetg](https://avatars.discourse-cdn.com/v4/letter/k/5f8ce5/32.png) [@konstantinetg](https://forum.inductiveautomation.com/u/konstantinetg)\
**Post date:** [March 27, 2026, 2:25pm UTC](https://forum.inductiveautomation.com/t/automation-professionals-ethernet-ip-communication-suite-v2/68190/202 "2026-03-27T14:25:54Z")

</div>

Hi,

I’m planning to use Ignition together with your driver for a project with an Omron NX102-9020 PLC. I expect to work with 100K+ tags.

Could you please advise which tools I should use to test the performance of the driver and my infrastructure? I’d like to better understand what level of performance I can realistically expect.

I’m still getting familiar with the platform, so any recommendations or best practices would be greatly appreciated.

Thank you in advance for your time!

[Previous page](https://forum.inductiveautomation.com/t/automation-professionals-ethernet-ip-communication-suite-v2/68190.md?page=9)