Hi All,

I have a remote BACnet device that is stuck on 'initializing.' It does not switch back and forth between 'initializing/uninitialized' it's simply stuck on 'initializing.' When I enable or disable the device an 'AddressSpaceNotRegistered' warning gets recorded in the logs. This remote device had been connecting fine. I've tried deleting and re-creating the device, restarting the BACnet module and even tried restarting the Gateway to no effect. As always, any help/info with this problem is greatly appreciated.

_IG version 8.1.32_

---

<div class="post-metadata">

**Author:** ![nicholas.gutt](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/nicholas.gutt/32/25670_2.png) [@nicholas.gutt](https://forum.inductiveautomation.com/u/nicholas.gutt)\
**Post date:** [May 27, 2026, 4:59pm UTC](https://forum.inductiveautomation.com/t/bacnet-device-wont-initialize/115731/2 "2026-05-27T16:59:54Z")

</div>

Is your BACNet device on the same subnet as your gateway?

---

<div class="post-metadata">

**Author:** ![harrison.m.freeman](https://avatars.discourse-cdn.com/v4/letter/h/54ee81/32.png) [@harrison.m.freeman](https://forum.inductiveautomation.com/u/harrison.m.freeman)\
**Post date:** [May 27, 2026, 5:19pm UTC](https://forum.inductiveautomation.com/t/bacnet-device-wont-initialize/115731/3 "2026-05-27T17:19:05Z")

</div>

No, it isn't. But I had been connected to it without issue. I've been using the '0.0.0.0' bind address successfully until today. I have multiple devices (all different subnets) still initialized/tags updating.

---

<div class="post-metadata">

**Author:** ![nicholas.gutt](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/nicholas.gutt/32/25670_2.png) [@nicholas.gutt](https://forum.inductiveautomation.com/u/nicholas.gutt)\
**Post date:** [May 27, 2026, 5:23pm UTC](https://forum.inductiveautomation.com/t/bacnet-device-wont-initialize/115731/4 "2026-05-27T17:23:09Z")

</div>

Been a few years since I connected BACNet devices but I had to manually update a device side file, like a routing table to get Ignition to connect. I believe the term was BBMD.

Any possibility your device has changed?

---

<div class="post-metadata">

**Author:** ![harrison.m.freeman](https://avatars.discourse-cdn.com/v4/letter/h/54ee81/32.png) [@harrison.m.freeman](https://forum.inductiveautomation.com/u/harrison.m.freeman)\
**Post date:** [May 27, 2026, 5:37pm UTC](https://forum.inductiveautomation.com/t/bacnet-device-wont-initialize/115731/5 "2026-05-27T17:37:56Z")

</div>

No, I don't think so, but I will check. Thank you for the direction.

---

<div class="post-metadata">

**Author:** ![nicholas.gutt](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/nicholas.gutt/32/25670_2.png) [@nicholas.gutt](https://forum.inductiveautomation.com/u/nicholas.gutt)\
**Post date:** [May 28, 2026, 12:37pm UTC](https://forum.inductiveautomation.com/t/bacnet-device-wont-initialize/115731/6 "2026-05-28T12:37:00Z")

</div>

I took a peek at a working setup. In the setup, gateway is on a different subnet than BACNet device. Below is config of local device. BBMD was updated on device side to include ip address of gateway.

Bind Address = ip address of gateway

Broadcast Address = device ip

BBMD Address = device ip

Device Number and Network number were obtained from the BACNet side.

---

<div class="post-metadata">

**Author:** ![harrison.m.freeman](https://avatars.discourse-cdn.com/v4/letter/h/54ee81/32.png) [@harrison.m.freeman](https://forum.inductiveautomation.com/u/harrison.m.freeman)\
**Post date:** [May 28, 2026, 12:58pm UTC](https://forum.inductiveautomation.com/t/bacnet-device-wont-initialize/115731/7 "2026-05-28T12:58:57Z")

</div>

Ok, thank you. In my organization, a different group owns/maintains the BMS, so I don't know how much luck I'll have with changing their setup. I'll look into it though. Thanks again!