# BACnet driver field level networks FLN

**URL:** <https://forum.inductiveautomation.com/t/bacnet-driver-field-level-networks-fln/44618>\
**Category:** Ignition\
**Created:** [March 18, 2021, 11:55am UTC](https://forum.inductiveautomation.com/t/bacnet-driver-field-level-networks-fln/44618 "2021-03-18T11:55:29Z")\
**Posts on this page:** 8\
**Page:** 1

<div class="post-metadata">

**Author:** ![eichler-eng](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/eichler-eng/32/21259_2.png) [@eichler-eng](https://forum.inductiveautomation.com/u/eichler-eng)\
**Post date:** [March 18, 2021, 11:55am UTC](https://forum.inductiveautomation.com/t/bacnet-driver-field-level-networks-fln/44618/1 "2021-03-18T11:55:29Z")

</div>

Hi all.

I am working on a BMS project with a lot of devices. I am new to BACnet. I have a few field panels behind which are field level networks with more devices. We are using Siemens equipment. I have added the field panels to ignition and, by using the BACnet driver, I can read data from the local IO of the field panel. However, I cannot see the FLN level devices. Please can someone suggest how to read data from the FLN?

Thanks  
Best regards

John

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [March 18, 2021, 12:44pm UTC](https://forum.inductiveautomation.com/t/bacnet-driver-field-level-networks-fln/44618/2 "2021-03-18T12:44:49Z")

</div>

They won’t just “show up” underneath the panel devices you added, you have to add a remote device instance for every one you’re interested in.

If the panel device acts as a BBMD you may need to specify that in your local device configuration before you can communicate with the FLN devices.

---

<div class="post-metadata">

**Author:** ![eichler-eng](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/eichler-eng/32/21259_2.png) [@eichler-eng](https://forum.inductiveautomation.com/u/eichler-eng)\
**Post date:** [March 19, 2021, 12:12am UTC](https://forum.inductiveautomation.com/t/bacnet-driver-field-level-networks-fln/44618/3 "2021-03-19T00:12:48Z")

</div>

Thanks Kevin. We have Siemens PXC panels. The panels are sending FLN data to a Desigo CC instance on the network but I’m struggling to get it into ignition. If I set up new remote points (in ignition) with the BACnet IDs for the FLN devices, they do not respond/initialize. I’ve also tried a third party BACnet explorer which was unable to locate the devices.

I will look into the configuration of the panels later today. Any other ideas?

Thanks again.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [March 19, 2021, 12:18am UTC](https://forum.inductiveautomation.com/t/bacnet-driver-field-level-networks-fln/44618/4 "2021-03-19T00:18:15Z")

</div>

Access to the FLN devices is going to be entirely dependent on the panel device either acting as a BBMD or relaying whoIs broadcasts to the FLN devices and then broadcasting their iAm responses back onto the network.

That a 3rd party BACnet explorer can’t see them either doesn’t bode well.

I don’t have much more advice to offer, I’m a bit of a BACnet n00b despite having worked on this driver.

---

<div class="post-metadata">

**Author:** ![eichler-eng](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/eichler-eng/32/21259_2.png) [@eichler-eng](https://forum.inductiveautomation.com/u/eichler-eng)\
**Post date:** [March 19, 2021, 12:22am UTC](https://forum.inductiveautomation.com/t/bacnet-driver-field-level-networks-fln/44618/5 "2021-03-19T00:22:23Z")

</div>

OK. I will see if I can find these settings in the panel config. I wondered if Desigo was communicating with the FLN devices via a proprietary protocol (not BACnet). Snip from the PXC compact manual:

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/3/c/3c3a3ec23ed9b3937f413d20fadc1c4807b15a9e.png)

I appreciate the help and I will report back with any findings.

---

<div class="post-metadata">

**Author:** ![kalmeida](https://avatars.discourse-cdn.com/v4/letter/k/b487fb/32.png) [@kalmeida](https://forum.inductiveautomation.com/u/kalmeida)\
**Post date:** [July 31, 2023, 11:16pm UTC](https://forum.inductiveautomation.com/t/bacnet-driver-field-level-networks-fln/44618/6 "2023-07-31T23:16:49Z")

</div>

@eichler-eng, were you able to work this out? I am in the same situation currently, and from what I have gathered, it _may_ be a BACnet Routing setting in the PXC Controllers, which can only be accessed via the Siemens ABT or SET software. Before I further my quest, I figured I would ask.

Thanks!

---

<div class="post-metadata">

**Author:** ![eichler-eng](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/eichler-eng/32/21259_2.png) [@eichler-eng](https://forum.inductiveautomation.com/u/eichler-eng)\
**Post date:** [January 27, 2024, 10:16am UTC](https://forum.inductiveautomation.com/t/bacnet-driver-field-level-networks-fln/44618/7 "2024-01-27T10:16:13Z")

</div>

Apologies for the very slow reply! Unfortunately, my client did not want to progress the project any further, so I never got to the bottom of the issue. Best of luck.

---

<div class="post-metadata">

**Author:** ![Jason.Miller](https://avatars.discourse-cdn.com/v4/letter/j/82dd89/32.png) [@Jason.Miller](https://forum.inductiveautomation.com/u/Jason.Miller)\
**Post date:** [May 6, 2025, 12:59pm UTC](https://forum.inductiveautomation.com/t/bacnet-driver-field-level-networks-fln/44618/8 "2025-05-06T12:59:35Z")

</div>

Hi guys, we are currently going through this as well. Have you come up with a solution? We have 3 Siemens PXC modular BACnet controllers which we are able to pull data from BUT we have 177 Siemens PXC IP, NON-BACnet controllers that we are not able to communicate to.  
Are there any integration drivers I am not seeing?

Thanks,  
Jason