# Bacnet Driver setup

**URL:** <https://forum.inductiveautomation.com/t/bacnet-driver-setup/53342>\
**Category:** Ignition\
**Tags:** perspective, ignition80\
**Created:** [November 22, 2021, 2:09pm UTC](https://forum.inductiveautomation.com/t/bacnet-driver-setup/53342 "2021-11-22T14:09:12Z")\
**Posts on this page:** 7\
**Page:** 1

<div class="post-metadata">

**Author:** ![tamerplc](https://avatars.discourse-cdn.com/v4/letter/t/d78d45/32.png) [@tamerplc](https://forum.inductiveautomation.com/u/tamerplc)\
**Post date:** [November 22, 2021, 2:09pm UTC](https://forum.inductiveautomation.com/t/bacnet-driver-setup/53342/1 "2021-11-22T14:09:13Z")

</div>

hi ,  
i am unable to establish communication between Gateway and BacNet devices .

below are teh seetings for local Bacnet

Gateway IP :10.4.132.11  
Bacnet Device : 10.10.83.52  
LocalBacnet address binding :0.0.0.0  
Local Bacnet Broadcast :10.4.132.254

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/0/f/0fdb759006a00848edfbaac1beaacf6357b12108.png)

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [November 22, 2021, 2:43pm UTC](https://forum.inductiveautomation.com/t/bacnet-driver-setup/53342/2 "2021-11-22T14:43:05Z")

</div>

With your device being on a different network than the gateway it’s unlikely you’ll be able to reach it with a broadcast message, and I can’t say for sure without knowing what the subnet mask is, but it seems unlikely that broadcast address would even include the remote device IP Anyway.

You may need a BBMD or some gateway device to bridge networks if you can’t get them onto the same network.

---

<div class="post-metadata">

**Author:** ![tamerplc](https://avatars.discourse-cdn.com/v4/letter/t/d78d45/32.png) [@tamerplc](https://forum.inductiveautomation.com/u/tamerplc)\
**Post date:** [November 22, 2021, 3:56pm UTC](https://forum.inductiveautomation.com/t/bacnet-driver-setup/53342/3 "2021-11-22T15:56:08Z")

</div>

Thanks Kevin  
I used below tools installed in same gateway server (different vlan) and able to browse all devices.  
[BACnet Explorer - Explore and manage your BACnet/IP devices](https://www.inneasoft.com/en/bacnet-explorer/).

So, what information needed from my network team to able to connect.

Thanks

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [November 22, 2021, 4:00pm UTC](https://forum.inductiveautomation.com/t/bacnet-driver-setup/53342/4 "2021-11-22T16:00:23Z")

</div>

I don’t know. Maybe you can work with support to compare Wireshark captures.

I can only tell you that Ignition must receive an “I-Am” response to the “Who-is” messages it sends both directly to the remote IP and to the broadcast address in order to establish comms. You have to figure out why that isn’t happening.

---

<div class="post-metadata">

**Author:** ![tamerplc](https://avatars.discourse-cdn.com/v4/letter/t/d78d45/32.png) [@tamerplc](https://forum.inductiveautomation.com/u/tamerplc)\
**Post date:** [November 22, 2021, 10:54pm UTC](https://forum.inductiveautomation.com/t/bacnet-driver-setup/53342/5 "2021-11-22T22:54:35Z")

</div>

Thanks Kevien for you guidance  
i am able to initilise the connection with BACnet devices .

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/f/b/fb18f21906d33ce5c911b1cc644496b937f8181e.png)

![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/9/0/9068766877c1cfaa183268b00edd00aff2be7a5b.png)

But getting below errors in logs. any guidance of that error meaning. the errors appears after I added BBMD Address

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/e/3/e3f43cc7b9cc5bd4efd59cf63105bc4ebeff8980.png)

---

<div class="post-metadata">

**Author:** ![djgilson](https://avatars.discourse-cdn.com/v4/letter/d/f14d63/32.png) [@djgilson](https://forum.inductiveautomation.com/u/djgilson)\
**Post date:** [May 20, 2022, 8:46pm UTC](https://forum.inductiveautomation.com/t/bacnet-driver-setup/53342/6 "2022-05-20T20:46:39Z")

</div>

Hi Tamerplc. Can you advice how you got this to initialize? I have a similar set up to yours, can cannot get it to initialize.

Thanks

---

<div class="post-metadata">

**Author:** ![Hana\_Bilowit](https://avatars.discourse-cdn.com/v4/letter/h/b4bc9f/32.png) [@Hana\_Bilowit](https://forum.inductiveautomation.com/u/Hana_Bilowit)\
**Post date:** [March 15, 2023, 11:06am UTC](https://forum.inductiveautomation.com/t/bacnet-driver-setup/53342/7 "2023-03-15T11:06:25Z")

</div>

Another gateway/server might be using prt 47808