New to Ignition. We are replacing the software used on our SCADA systems from Cimplicity to Ignition.

With Cimplicity, in order to send collected data to a Building automation system via BACnet, we had to utilize an external Modbus RTU to BACnet gateway. Is there a way to utilize the BACnet feature of Ignition to act as this gateway instead of using an external unit?

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [May 15, 2024, 9:00pm UTC](https://forum.inductiveautomation.com/t/bacnet-driver-used-at-a-modbus-to-bacnet-gateway/90461/2 "2024-05-15T21:00:13Z")

</div>

No, it can't act as a Modbus RTU to BACnet gateway.

Why do you need the gateway at all? Is the BACnet stuff all on another network you can't reach or did Cimplicity not have a BACnet driver?

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [May 15, 2024, 10:03pm UTC](https://forum.inductiveautomation.com/t/bacnet-driver-used-at-a-modbus-to-bacnet-gateway/90461/3 "2024-05-15T22:03:00Z")

</div>

Well, you could add my alternate Modbus driver and set it up to be a Modbus RTU slave. It would need a fair amount of scripting to move data in both directions, but it is certainly possible. This topic might help:

> [@Modbus Slave/Server to Generate Read Only Tags](https://forum.inductiveautomation.com/t/modbus-slave-server-to-generate-read-only-tags/87583/21):
>
> I've create a generic "Modbus Publish" script that eliminates the need for a second set of tags. I've publicly posted it here: [https://www.automation-pros.com/ignition/modbusPublish.py](https://www.automation-pros.com/ignition/modbusPublish.py) It requires the "Queue Utility" script posted here: [https://www.automation-pros.com/ignition/queueUtil.py](https://www.automation-pros.com/ignition/queueUtil.py) and described over here: Both scripts rely on my Integration Toolkit's globalVarMap() script function, but you can rework that (not quite 1:1) to use system.util.getGlobals() if you must. (Not recomme…