# Batchoperations flood of errors

**URL:** <https://forum.inductiveautomation.com/t/batchoperations-flood-of-errors/40292>\
**Category:** Ignition\
**Tags:** ignition80\
**Created:** [November 4, 2020, 1:58pm UTC](https://forum.inductiveautomation.com/t/batchoperations-flood-of-errors/40292 "2020-11-04T13:58:05Z")\
**Posts on this page:** 20\
**Page:** 1

<div class="post-metadata">

**Author:** ![ryanjmclaughlin](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/ryanjmclaughlin/32/4318_2.png) [@ryanjmclaughlin](https://forum.inductiveautomation.com/u/ryanjmclaughlin)\
**Post date:** [November 4, 2020, 1:58pm UTC](https://forum.inductiveautomation.com/t/batchoperations-flood-of-errors/40292/1 "2020-11-04T13:58:05Z")

</div>

In 8.0.16, I am getting a ton of logs under the tags.storage.batchoperations. Any ideas on what is going on here? It seems like something is corrupted with my tag provider, but not sure how I can fix it…

```auto
simpleorm.utils.SException$Error: Cannot access destroyed record [InternalJsonStorageInfoRecord [Destroyed SRecordInstance] Dirty-2]
at simpleorm.dataset.SRecordInstance.checkFieldIsAccessible(SRecordInstance.java:233)
at simpleorm.dataset.SRecordInstance.setObject(SRecordInstance.java:255)
at simpleorm.dataset.SRecordInstance.setObject(SRecordInstance.java:248)
at simpleorm.dataset.SRecordInstance.setString(SRecordInstance.java:424)
at com.inductiveautomation.ignition.gateway.tags.config.storage.internaljson.InternalJsonStorageInfoRecord.setVersion(InternalJsonStorageInfoRecord.java:35)
at com.inductiveautomation.ignition.gateway.tags.config.storage.internaljson.InternalJsonStorageManager.saveVersion(InternalJsonStorageManager.java:90)
at com.inductiveautomation.ignition.gateway.tags.config.storage.internaljson.InternalJsonStorageManager$RedundantTagSynchronizationProvider.setVersion(InternalJsonStorageManager.java:592)
at com.inductiveautomation.ignition.gateway.redundancy.types.AbstractSynchronizedStateProvider.incrementVersion(AbstractSynchronizedStateProvider.java:93)
at com.inductiveautomation.ignition.gateway.tags.config.storage.internaljson.InternalJsonStorageManager$RedundantTagSynchronizationProvider.processChanges(InternalJsonStorageManager.java:640)
at com.inductiveautomation.ignition.gateway.tags.config.storage.internaljson.InternalJsonStorageManager.save(InternalJsonStorageManager.java:181)
at com.inductiveautomation.ignition.gateway.tags.config.BatchConfigOperation.execute(BatchConfigOperation.java:100)
at com.inductiveautomation.ignition.gateway.tags.evaluation.BatchContextImpl$OpController.run(BatchContextImpl.java:187)
at java.base/java.util.concurrent.Executors$RunnableAdapter.call(Unknown Source)
at java.base/java.util.concurrent.FutureTask.run(Unknown Source)
at java.base/java.util.concurrent.ScheduledThreadPoolExecutor$ScheduledFutureTask.run(Unknown Source)
at java.base/java.util.concurrent.ThreadPoolExecutor.runWorker(Unknown Source)
at java.base/java.util.concurrent.ThreadPoolExecutor$Worker.run(Unknown Source)
at java.base/java.lang.Thread.run(Unknown Source)

```

---

<div class="post-metadata">

**Author:** ![adam.todorski](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/adam.todorski/32/19388_2.png) [@adam.todorski](https://forum.inductiveautomation.com/u/adam.todorski)\
**Post date:** [November 10, 2020, 6:02pm UTC](https://forum.inductiveautomation.com/t/batchoperations-flood-of-errors/40292/2 "2020-11-10T18:02:01Z")

</div>

I’ve also seen this alongside some pretty scary stability issues with the platform itself (installed licenses disappearing, HTTP 500 errors when trying to get into the gateway web UI, connected designer sessions locking up). This was on a dev system that gets flogged with major changes all the time for me so I assumed we had created some bad sequence of peering it with other gateways then having those gateways go away or something along those lines to cause it, but the only clue I have is that the internal DB appears to be inaccessible by parts of the system:

INFO | jvm 1 | 2020/11/10 17:51:09 | E [t.s.internaljson] [17:51:09]: Errror storing tag changes. provider=default  
INFO | jvm 1 | 2020/11/10 17:51:09 | simpleorm.utils.SException$Jdbc: Executing UPDATE tagconfig SET cfg = ? WHERE id = ? AND cfg = ? for [TagConfigurationRecord 46ae0157-c826-4e2b-ac9c-7628c7e8d257.5462bb3f-1b41-47ce-9d30-77bfd1bcda1c Dirty0]  
INFO | jvm 1 | 2020/11/10 17:51:09 | at simpleorm.sessionjdbc.SSessionJdbcHelper.flushExecuteUpdate(SSessionJdbcHelper.java:434)  
INFO | jvm 1 | 2020/11/10 17:51:09 | at simpleorm.sessionjdbc.SSessionJdbcHelper.flush(SSessionJdbcHelper.java:400)  
INFO | jvm 1 | 2020/11/10 17:51:09 | at simpleorm.sessionjdbc.SSessionJdbc.flush(SSessionJdbc.java:459)  
INFO | jvm 1 | 2020/11/10 17:51:09 | at simpleorm.sessionjdbc.SSessionJdbc.flush(SSessionJdbc.java:443)  
INFO | jvm 1 | 2020/11/10 17:51:09 | at simpleorm.sessionjdbc.SSessionJdbc.commit(SSessionJdbc.java:375)  
INFO | jvm 1 | 2020/11/10 17:51:09 | at com.inductiveautomation.ignition.gateway.tags.config.storage.internaljson.InternalJsonStorageManager.saveInternal(InternalJsonStorageManager.java:286)  
INFO | jvm 1 | 2020/11/10 17:51:09 | at com.inductiveautomation.ignition.gateway.tags.config.storage.internaljson.InternalJsonStorageManager$IndependantTagSynchronizationProvider.processChanges(InternalJsonStorageManager.java:532)  
INFO | jvm 1 | 2020/11/10 17:51:09 | at com.inductiveautomation.ignition.gateway.tags.config.storage.internaljson.InternalJsonStorageManager$RedundantTagSynchronizationProvider.processChanges(InternalJsonStorageManager.java:622)  
INFO | jvm 1 | 2020/11/10 17:51:09 | at com.inductiveautomation.ignition.gateway.tags.config.storage.internaljson.InternalJsonStorageManager.save(InternalJsonStorageManager.java:181)  
INFO | jvm 1 | 2020/11/10 17:51:09 | at com.inductiveautomation.ignition.gateway.tags.config.BatchConfigOperation.execute(BatchConfigOperation.java:100)  
INFO | jvm 1 | 2020/11/10 17:51:09 | at com.inductiveautomation.ignition.gateway.tags.evaluation.BatchContextImpl$OpController.run(BatchContextImpl.java:187)  
INFO | jvm 1 | 2020/11/10 17:51:09 | at java.base/java.util.concurrent.Executors$RunnableAdapter.call(Unknown Source)  
INFO | jvm 1 | 2020/11/10 17:51:09 | at java.base/java.util.concurrent.FutureTask.run(Unknown Source)  
INFO | jvm 1 | 2020/11/10 17:51:09 | at java.base/java.util.concurrent.ScheduledThreadPoolExecutor$ScheduledFutureTask.run(Unknown Source)  
INFO | jvm 1 | 2020/11/10 17:51:09 | at java.base/java.util.concurrent.ThreadPoolExecutor.runWorker(Unknown Source)  
INFO | jvm 1 | 2020/11/10 17:51:09 | at java.base/java.util.concurrent.ThreadPoolExecutor$Worker.run(Unknown Source)  
INFO | jvm 1 | 2020/11/10 17:51:09 | at java.base/java.lang.Thread.run(Unknown Source)  
INFO | jvm 1 | 2020/11/10 17:51:09 | Suppressed: simpleorm.utils.SException$Jdbc: Executing UPDATE tagconfig SET cfg = ? WHERE id = ? AND cfg = ? for [TagConfigurationRecord 4e6678a1-e4ce-4015-ae7b-06cba77ffb05.58a6a5de-1130-4258-b1a9-bb3415003a7b Dirty1]  
INFO | jvm 1 | 2020/11/10 17:51:09 | at simpleorm.sessionjdbc.SSessionJdbcHelper.flushExecuteUpdate(SSessionJdbcHelper.java:434)  
INFO | jvm 1 | 2020/11/10 17:51:09 | at simpleorm.sessionjdbc.SSessionJdbcHelper.flush(SSessionJdbcHelper.java:400)  
INFO | jvm 1 | 2020/11/10 17:51:09 | at simpleorm.sessionjdbc.SSessionJdbc.flush(SSessionJdbc.java:459)  
INFO | jvm 1 | 2020/11/10 17:51:09 | at simpleorm.sessionjdbc.SSessionJdbc.flush(SSessionJdbc.java:443)  
INFO | jvm 1 | 2020/11/10 17:51:09 | at simpleorm.sessionjdbc.SSessionJdbc.commitAndDetachDataSet(SSessionJdbc.java:382)  
INFO | jvm 1 | 2020/11/10 17:51:09 | at com.inductiveautomation.ignition.gateway.localdb.persistence.PersistenceSession.close(PersistenceSession.java:61)  
INFO | jvm 1 | 2020/11/10 17:51:09 | at com.inductiveautomation.ignition.gateway.tags.config.storage.internaljson.InternalJsonStorageManager.saveInternal(InternalJsonStorageManager.java:284)  
INFO | jvm 1 | 2020/11/10 17:51:09 | … 11 common frames omitted  
INFO | jvm 1 | 2020/11/10 17:51:09 | Caused by: org.sqlite.SQLiteException: [SQLITE\_CANTOPEN] Unable to open the database file (unable to open database file)  
INFO | jvm 1 | 2020/11/10 17:51:09 | at org.sqlite.core.DB.newSQLException(DB.java:909)  
INFO | jvm 1 | 2020/11/10 17:51:09 | at org.sqlite.core.DB.newSQLException(DB.java:921)  
INFO | jvm 1 | 2020/11/10 17:51:09 | at org.sqlite.core.DB.execute(DB.java:825)  
INFO | jvm 1 | 2020/11/10 17:51:09 | at org.sqlite.core.DB.executeUpdate(DB.java:863)  
INFO | jvm 1 | 2020/11/10 17:51:09 | at org.sqlite.jdbc3.JDBC3PreparedStatement.executeUpdate(JDBC3PreparedStatement.java:102)  
INFO | jvm 1 | 2020/11/10 17:51:09 | at simpleorm.sessionjdbc.SSessionJdbcHelper.flushExecuteUpdate(SSessionJdbcHelper.java:432)  
INFO | jvm 1 | 2020/11/10 17:51:09 | … 17 common frames omitted  
INFO | jvm 1 | 2020/11/10 17:51:09 | Caused by: org.sqlite.SQLiteException: [SQLITE\_CANTOPEN] Unable to open the database file (unable to open database file)  
INFO | jvm 1 | 2020/11/10 17:51:09 | at org.sqlite.core.DB.newSQLException(DB.java:909)  
INFO | jvm 1 | 2020/11/10 17:51:09 | at org.sqlite.core.DB.newSQLException(DB.java:921)  
INFO | jvm 1 | 2020/11/10 17:51:09 | at org.sqlite.core.DB.execute(DB.java:825)  
INFO | jvm 1 | 2020/11/10 17:51:09 | at org.sqlite.core.DB.executeUpdate(DB.java:863)  
INFO | jvm 1 | 2020/11/10 17:51:09 | at org.sqlite.jdbc3.JDBC3PreparedStatement.executeUpdate(JDBC3PreparedStatement.java:102)  
INFO | jvm 1 | 2020/11/10 17:51:09 | at simpleorm.sessionjdbc.SSessionJdbcHelper.flushExecuteUpdate(SSessionJdbcHelper.java:432)  
INFO | jvm 1 | 2020/11/10 17:51:09 | … 16 common frames omitted

---

<div class="post-metadata">

**Author:** ![ryanjmclaughlin](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/ryanjmclaughlin/32/4318_2.png) [@ryanjmclaughlin](https://forum.inductiveautomation.com/u/ryanjmclaughlin)\
**Post date:** [November 10, 2020, 6:48pm UTC](https://forum.inductiveautomation.com/t/batchoperations-flood-of-errors/40292/3 "2020-11-10T18:48:39Z")

</div>

Support reviewed this for me and it sounded as its a known issue. A gateway restart fixed it for me, still not sure the root cause.

---

<div class="post-metadata">

**Author:** ![adam.todorski](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/adam.todorski/32/19388_2.png) [@adam.todorski](https://forum.inductiveautomation.com/u/adam.todorski)\
**Post date:** [November 10, 2020, 6:58pm UTC](https://forum.inductiveautomation.com/t/batchoperations-flood-of-errors/40292/4 "2020-11-10T18:58:10Z")

</div>

Same here with the GW restart fixing it, did they give you an indication of what version may have the bug fix?

---

<div class="post-metadata">

**Author:** ![Gaurav.Shitole](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/gaurav.shitole/32/72050_2.png) [@Gaurav.Shitole](https://forum.inductiveautomation.com/u/Gaurav.Shitole)\
**Post date:** [October 20, 2021, 7:25am UTC](https://forum.inductiveautomation.com/t/batchoperations-flood-of-errors/40292/5 "2021-10-20T07:25:26Z")

</div>

Hello, is there any update on this?

I am using version 8.1.1 and still facing this issue.

---

<div class="post-metadata">

**Author:** ![ryanjmclaughlin](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/ryanjmclaughlin/32/4318_2.png) [@ryanjmclaughlin](https://forum.inductiveautomation.com/u/ryanjmclaughlin)\
**Post date:** [October 21, 2021, 1:24pm UTC](https://forum.inductiveautomation.com/t/batchoperations-flood-of-errors/40292/6 "2021-10-21T13:24:19Z")

</div>

This was fixed in the current release of Ignition. Suggest you update from 8.1.1 to 8.1.11

---

<div class="post-metadata">

**Author:** ![Gaurav.Shitole](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/gaurav.shitole/32/72050_2.png) [@Gaurav.Shitole](https://forum.inductiveautomation.com/u/Gaurav.Shitole)\
**Post date:** [October 21, 2021, 7:29pm UTC](https://forum.inductiveautomation.com/t/batchoperations-flood-of-errors/40292/7 "2021-10-21T19:29:50Z")

</div>

Okay thanks for the update

---

<div class="post-metadata">

**Author:** ![martinel3746](https://avatars.discourse-cdn.com/v4/letter/m/e0b2c6/32.png) [@martinel3746](https://forum.inductiveautomation.com/u/martinel3746)\
**Post date:** [March 3, 2022, 4:02am UTC](https://forum.inductiveautomation.com/t/batchoperations-flood-of-errors/40292/8 "2022-03-03T04:02:07Z")

</div>

I’m seeing the same issue in 8.1.14.  
Tech support said to reboot the gateway.  
I stopped and restarted the service and it helped for a day.  
I’ll reboot the server this weekend and see if that helps.

---

<div class="post-metadata">

**Author:** ![rbachman](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/rbachman/32/43718_2.png) [@rbachman](https://forum.inductiveautomation.com/u/rbachman)\
**Post date:** [March 11, 2022, 5:28pm UTC](https://forum.inductiveautomation.com/t/batchoperations-flood-of-errors/40292/9 "2022-03-11T17:28:49Z")

</div>

I’m seeing this for the first time today. We plan to reboot the server this weekend to see if that will help. It would be nice to know if there is a known cause so we can address the root issue.

---

<div class="post-metadata">

**Author:** ![martinel3746](https://avatars.discourse-cdn.com/v4/letter/m/e0b2c6/32.png) [@martinel3746](https://forum.inductiveautomation.com/u/martinel3746)\
**Post date:** [March 14, 2022, 4:27pm UTC](https://forum.inductiveautomation.com/t/batchoperations-flood-of-errors/40292/10 "2022-03-14T16:27:27Z")

</div>

I have an open ticket for this.  
I was told that there was a fix for this in 8.1.15.  
After updating from 8.1.14 to 8.1.15 and rebooting the server we now get 3 errors per second.  
This server is very simple, using all defaults (except user source), only 24 devices, one UDT and one daily scheduled process.

---

<div class="post-metadata">

**Author:** ![John\_S1](https://avatars.discourse-cdn.com/v4/letter/j/c0e974/32.png) [@John\_S1](https://forum.inductiveautomation.com/u/John_S1)\
**Post date:** [September 7, 2022, 3:12pm UTC](https://forum.inductiveautomation.com/t/batchoperations-flood-of-errors/40292/11 "2022-09-07T15:12:53Z")

</div>

Hi did you find any solution for this from IA team.

---

<div class="post-metadata">

**Author:** ![martinel3746](https://avatars.discourse-cdn.com/v4/letter/m/e0b2c6/32.png) [@martinel3746](https://forum.inductiveautomation.com/u/martinel3746)\
**Post date:** [September 7, 2022, 4:33pm UTC](https://forum.inductiveautomation.com/t/batchoperations-flood-of-errors/40292/12 "2022-09-07T16:33:37Z")

</div>

No.  
I’ve upgraded to 8.1.17 and it’s still there.  
It doesn’t seem to impact performance for this server and so far hasn’t shown up on any of our other 130+ gateways. I ran out of energy and got tired of chasing it so had the ticket closed.  
Every time it flares up, usually ~two days after a gateway startup, I go to the Log Configuration and turn off the “ **tags.\*.batchoperations** ” loggers.

---

<div class="post-metadata">

**Author:** ![bprice](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/bprice/32/83520_2.png) [@bprice](https://forum.inductiveautomation.com/u/bprice)\
**Post date:** [December 16, 2022, 10:04pm UTC](https://forum.inductiveautomation.com/t/batchoperations-flood-of-errors/40292/13 "2022-12-16T22:04:05Z")

</div>

I'm not sure when this error persisted for our system. But we are on Version 8.1.18 and this is the first time it has caught my attention. Hoping to be able to restart the gateway soon, as I don't have administrative access on our new server at the moment.

---

<div class="post-metadata">

**Author:** ![louagejasper](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/louagejasper/32/86311_2.png) [@louagejasper](https://forum.inductiveautomation.com/u/louagejasper)\
**Post date:** [February 24, 2023, 2:30pm UTC](https://forum.inductiveautomation.com/t/batchoperations-flood-of-errors/40292/14 "2023-02-24T14:30:55Z")

</div>

I'm having this on 8.1.24.

---

<div class="post-metadata">

**Author:** ![Isaac\_Hodgkins](https://avatars.discourse-cdn.com/v4/letter/i/59ef9b/32.png) [@Isaac\_Hodgkins](https://forum.inductiveautomation.com/u/Isaac_Hodgkins)\
**Post date:** [June 5, 2023, 2:39pm UTC](https://forum.inductiveautomation.com/t/batchoperations-flood-of-errors/40292/15 "2023-06-05T14:39:50Z")

</div>

I'm having this on 8.1.22

---

<div class="post-metadata">

**Author:** ![Transistor](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/transistor/32/3380_2.png) [@Transistor](https://forum.inductiveautomation.com/u/Transistor)\
**Post date:** [June 5, 2023, 2:46pm UTC](https://forum.inductiveautomation.com/t/batchoperations-flood-of-errors/40292/16 "2023-06-05T14:46:42Z")

</div>

Me too on 8.1.26. I'm having to restart the gateway any time I need to use the logs for debugging.

---

<div class="post-metadata">

**Author:** ![ryanjmclaughlin](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/ryanjmclaughlin/32/4318_2.png) [@ryanjmclaughlin](https://forum.inductiveautomation.com/u/ryanjmclaughlin)\
**Post date:** [June 5, 2023, 2:53pm UTC](https://forum.inductiveautomation.com/t/batchoperations-flood-of-errors/40292/17 "2023-06-05T14:53:06Z")

</div>

Upgraded to 8.1.28 and still an issue ☹

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/d/5/d555de7a45d19098ffa9c71dcbf23279eacef36a.png)

---

<div class="post-metadata">

**Author:** ![ironyeti1](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/ironyeti1/32/36635_2.png) [@ironyeti1](https://forum.inductiveautomation.com/u/ironyeti1)\
**Post date:** [June 26, 2023, 7:01pm UTC](https://forum.inductiveautomation.com/t/batchoperations-flood-of-errors/40292/18 "2023-06-26T19:01:03Z")

</div>

I think this will have to be the permanent solution 😮‍💨

---

<div class="post-metadata">

**Author:** ![Anthony\_Granato](https://avatars.discourse-cdn.com/v4/letter/a/9dc877/32.png) [@Anthony\_Granato](https://forum.inductiveautomation.com/u/Anthony_Granato)\
**Post date:** [August 15, 2023, 8:20pm UTC](https://forum.inductiveautomation.com/t/batchoperations-flood-of-errors/40292/19 "2023-08-15T20:20:28Z")

</div>

Agreed. The Log Configuration settings apply to all users, so it is not a bad one either... for now at least. Just need to be careful and have awareness

---

<div class="post-metadata">

**Author:** ![avaughn](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/avaughn/32/38972_2.png) [@avaughn](https://forum.inductiveautomation.com/u/avaughn)\
**Post date:** [August 29, 2023, 10:09pm UTC](https://forum.inductiveautomation.com/t/batchoperations-flood-of-errors/40292/20 "2023-08-29T22:09:37Z")

</div>

There should be a fix for this in 8.1.32 RC1 which is currently available to [download](https://inductiveautomation.com/downloads/ignition/8.1.32-rc1) for testing.

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/2/6/26a07e426138ff7c8f715f69d09e5aa28f707cc8.png)  
Screenshot from the [8.1.32 RC1 Release Notes](https://inductiveautomation.com/downloads/releasenotes/8.1.32-rc1)

[Next page](https://forum.inductiveautomation.com/t/batchoperations-flood-of-errors/40292.md?page=2)