# Best way to detect PLC, sensor disconnection

**URL:** <https://forum.inductiveautomation.com/t/best-way-to-detect-plc-sensor-disconnection/8310>\
**Category:** General Discussion\
**Created:** [April 15, 2014, 11:48am UTC](https://forum.inductiveautomation.com/t/best-way-to-detect-plc-sensor-disconnection/8310 "2014-04-15T11:48:58Z")\
**Posts on this page:** 3\
**Page:** 1

<div class="post-metadata">

**Author:** ![lvboque](https://avatars.discourse-cdn.com/v4/letter/l/9f8e36/32.png) [@lvboque](https://forum.inductiveautomation.com/u/lvboque)\
**Post date:** [April 15, 2014, 11:48am UTC](https://forum.inductiveautomation.com/t/best-way-to-detect-plc-sensor-disconnection/8310/1 "2014-04-15T11:48:58Z")

</div>

Hello,

Is it possible to detect the disconnection of a PLC using the prosys OPC Client and Ignition OPC Server?  
Is it possible to get callback when the PLC is disconnected?

What about sensor? Is it possible to detect a disconnection of a temperature sensor as example?

Thanks for your advices,

---

<div class="post-metadata">

**Author:** ![greg.simpson](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/greg.simpson/32/3135_2.png) [@greg.simpson](https://forum.inductiveautomation.com/u/greg.simpson)\
**Post date:** [April 25, 2014, 5:04pm UTC](https://forum.inductiveautomation.com/t/best-way-to-detect-plc-sensor-disconnection/8310/2 "2014-04-25T17:04:14Z")

</div>

The temp sensor I am not sure about.

You could potentially look at the quality of the tags you are monitoring. You could then alarm off of that. There is also a diagnostics folder that contains a tag called “Connection State”. You could use this as well.

---

<div class="post-metadata">

**Author:** ![Dravik](https://avatars.discourse-cdn.com/v4/letter/d/e274bd/32.png) [@Dravik](https://forum.inductiveautomation.com/u/Dravik)\
**Post date:** [April 25, 2014, 8:36pm UTC](https://forum.inductiveautomation.com/t/best-way-to-detect-plc-sensor-disconnection/8310/3 "2014-04-25T20:36:24Z")

</div>

If it is 4-20ma, You can alarm when it is below 4ma.

Thermocouples usually read max when disconnected, can alarm on that.

Depends!