Does your OPC-UA Device driver for controllogix allow me to bridge through a controllogix backplane from one ENBT to another ENBT and access a processor on that subnet? ie. I’ve got one ENBT in slot 3 with an addy of 130.100.70.70 and I’d like to bridge to an ENBT in slot 0 to access a processor in slot 6 in a remote chassis with an ENBT addy of 172.20.1.184?  
I tried to configure the driver using a Hostname of 130.100.70.70 and a connection string of 1,[0,2,172.20.1.184,1],6. The device status shows connected, but I can’t browse any tags.

---

<div class="post-metadata">

**Author:** ![f\_jons](https://avatars.discourse-cdn.com/v4/letter/f/9fc29f/32.png) [@f\_jons](https://forum.inductiveautomation.com/u/f_jons)\
**Post date:** [January 18, 2011, 1:49pm UTC](https://forum.inductiveautomation.com/t/bridging-through-controllogix-backplane-to-another-subnet/2522/2 "2011-01-18T13:49:04Z")

</div>

I called tech support about this very problem a few months ago and no resolution was found. This is a feature I will need in the next month or so.

---

<div class="post-metadata">

**Author:** ![thechtman](https://avatars.discourse-cdn.com/v4/letter/t/e56c9b/32.png) [@thechtman](https://forum.inductiveautomation.com/u/thechtman)\
**Post date:** [January 18, 2011, 6:46pm UTC](https://forum.inductiveautomation.com/t/bridging-through-controllogix-backplane-to-another-subnet/2522/3 "2011-01-18T18:46:27Z")

</div>

It currently is not supported, but will be added in the next month.

---

<div class="post-metadata">

**Author:** ![Jon.Trusik](https://avatars.discourse-cdn.com/v4/letter/j/d78d45/32.png) [@Jon.Trusik](https://forum.inductiveautomation.com/u/Jon.Trusik)\
**Post date:** [January 19, 2011, 11:46am UTC](https://forum.inductiveautomation.com/t/bridging-through-controllogix-backplane-to-another-subnet/2522/4 "2011-01-19T11:46:48Z")

</div>

OK, thanks!

---

<div class="post-metadata">

**Author:** ![f\_jons](https://avatars.discourse-cdn.com/v4/letter/f/9fc29f/32.png) [@f\_jons](https://forum.inductiveautomation.com/u/f_jons)\
**Post date:** [March 22, 2011, 7:42pm UTC](https://forum.inductiveautomation.com/t/bridging-through-controllogix-backplane-to-another-subnet/2522/5 "2011-03-22T19:42:11Z")

</div>

Has this feature been added yet?

---

<div class="post-metadata">

**Author:** ![thechtman](https://avatars.discourse-cdn.com/v4/letter/t/e56c9b/32.png) [@thechtman](https://forum.inductiveautomation.com/u/thechtman)\
**Post date:** [March 23, 2011, 8:59pm UTC](https://forum.inductiveautomation.com/t/bridging-through-controllogix-backplane-to-another-subnet/2522/6 "2011-03-23T20:59:11Z")

</div>

It is very close for the ControlLogix and CompactLogix processors. Next will be the PLC, SLC and MicroLogix.

I’ll keep you posted.

---

<div class="post-metadata">

**Author:** ![f\_jons](https://avatars.discourse-cdn.com/v4/letter/f/9fc29f/32.png) [@f\_jons](https://forum.inductiveautomation.com/u/f_jons)\
**Post date:** [March 23, 2011, 9:56pm UTC](https://forum.inductiveautomation.com/t/bridging-through-controllogix-backplane-to-another-subnet/2522/7 "2011-03-23T21:56:14Z")

</div>

Thank you !

---

<div class="post-metadata">

**Author:** ![f\_jons](https://avatars.discourse-cdn.com/v4/letter/f/9fc29f/32.png) [@f\_jons](https://forum.inductiveautomation.com/u/f_jons)\
**Post date:** [April 26, 2011, 4:42pm UTC](https://forum.inductiveautomation.com/t/bridging-through-controllogix-backplane-to-another-subnet/2522/8 "2011-04-26T16:42:59Z")

</div>

Status Update? Otherwise we will need to look into switching back to Kepware for this functionality.

---

<div class="post-metadata">

**Author:** ![thechtman](https://avatars.discourse-cdn.com/v4/letter/t/e56c9b/32.png) [@thechtman](https://forum.inductiveautomation.com/u/thechtman)\
**Post date:** [April 29, 2011, 4:33pm UTC](https://forum.inductiveautomation.com/t/bridging-through-controllogix-backplane-to-another-subnet/2522/9 "2011-04-29T16:33:24Z")

</div>

Yes, we have bridging to another subnet through a ControlLogix gateway working in-house for ControlLogix, CompactLogix and SLC processors.

I’ll be wrapping it up and pushing it out to the beta soon.

Tom

---

<div class="post-metadata">

**Author:** ![AlexW](https://avatars.discourse-cdn.com/v4/letter/a/b5a626/32.png) [@AlexW](https://forum.inductiveautomation.com/u/AlexW)\
**Post date:** [April 29, 2011, 5:40pm UTC](https://forum.inductiveautomation.com/t/bridging-through-controllogix-backplane-to-another-subnet/2522/10 "2011-04-29T17:40:06Z")

</div>

How about the following route?  
ethernet  
1756-ENBT  
Controllogix backplane  
1756-DHRIO  
DH+  
SLC?

We can use RSLinx otherwise I guess

Edit: Its possible, I found the answer in the user manual