# \[BUG 15126,15127\] Alarm Status Table - Alarm Details empty & Ack Alarms - Remote server

**URL:** <https://forum.inductiveautomation.com/t/bug-15126-15127-alarm-status-table-alarm-details-empty-ack-alarms-remote-server/28563>\
**Category:** Ignition Early Access\
**Created:** [September 26, 2019, 5:49am UTC](https://forum.inductiveautomation.com/t/bug-15126-15127-alarm-status-table-alarm-details-empty-ack-alarms-remote-server/28563 "2019-09-26T05:49:54Z")\
**Posts on this page:** 3\
**Page:** 1

<div class="post-metadata">

**Author:** ![Tumeksi](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/tumeksi/32/4697_2.png) [@Tumeksi](https://forum.inductiveautomation.com/u/Tumeksi)\
**Post date:** [September 26, 2019, 5:49am UTC](https://forum.inductiveautomation.com/t/bug-15126-15127-alarm-status-table-alarm-details-empty-ack-alarms-remote-server/28563/1 "2019-09-26T05:49:54Z")

</div>

Hi,

We have a front-end server and an IO server setup.  
We have set alarms on tags on the IO server and show them on the FE server on the Alarm status table.  
On these alarms the “Alarm details” popup is empty.  
Also if we set the alarm to “ack notes required” ON and try to ack the alarms, the alarm is acked and no input is required.

If we set up a tag on the FE server and set alarms on that everything works as it should (details show up and ack notes are required)

FE version: 8 b2019091302  
IO version: 8 b2019082602

The remote tag provider is set:  
“Alarms Enabled”: True  
“Alarm Mode”: Queried

---

<div class="post-metadata">

**Author:** ![dmalan](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/dmalan/32/10600_2.png) [@dmalan](https://forum.inductiveautomation.com/u/dmalan)\
**Post date:** [September 27, 2019, 11:09pm UTC](https://forum.inductiveautomation.com/t/bug-15126-15127-alarm-status-table-alarm-details-empty-ack-alarms-remote-server/28563/2 "2019-09-27T23:09:42Z")

</div>

Thank you for the information. I have been able to replicate the issue and will be creating bug tickets for both issues. I was only able to replicate this in a Perspective session. In a Vision window, this is not an issue.

---

<div class="post-metadata">

**Author:** ![paul-griffith](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/paul-griffith/32/37249_2.png) [@paul-griffith](https://forum.inductiveautomation.com/u/paul-griffith)\
**Post date:** [May 8, 2020, 4:38pm UTC](https://forum.inductiveautomation.com/t/bug-15126-15127-alarm-status-table-alarm-details-empty-ack-alarms-remote-server/28563/3 "2020-05-08T16:38:09Z")

</div>

> [@Tumeksi](#):
>
> We have set alarms on tags on the IO server and show them on the FE server on the Alarm status table.  
> On these alarms the “Alarm details” popup is empty.

This issue has been fixed for 8.0.13; the other is still in progress.