**Post date:** [August 23, 2022, 6:36am UTC](https://forum.inductiveautomation.com/t/bug-number-of-shelving-times-can-not-be-changed-in-alarm-status-table-in-perspective/63313/1 "2022-08-23T06:36:16Z")

</div>

Hi,

When changing the number of shelving times in the Alarm Status Table in Ignition Perspective the component adds an additional time of one of the existing ones.

In this case I removed the first time which was 30 minutes (value of 1800). That way I only have 5 shelving times.  
 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/4/f/4f81ffe8a435531f19210a1e76a0f799fc3394e5.png)

But when I run this in the browser I see that “4 hours” are added in the bottom of the list so I have a total of 6 times again.  
 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/c/5/c578e39a96a984ae7cfcbbbec9e26078110ee3df.png)

If I save the view with only 5 shelving times and close it and open it again in the designer I also see that a sixth time is being added.

---

<div class="post-metadata">

**Author:** ![user77](https://avatars.discourse-cdn.com/v4/letter/u/a183cd/32.png) [@user77](https://forum.inductiveautomation.com/u/user77)\
**Post date:** [August 23, 2022, 7:03am UTC](https://forum.inductiveautomation.com/t/bug-number-of-shelving-times-can-not-be-changed-in-alarm-status-table-in-perspective/63313/2 "2022-08-23T07:03:09Z")

</div>

This sounds like a persistence issue.

1. Set the values as non-persistent that you do not want.

![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/1/2/1242fc58c708a9b748705f8d89739d5f63e61861.png)

![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/6/f/6fda0a50b111bc6f47edc2b0b61972b38751592a.png)

1. Save and close the view. Reopen the view, you should see null values.

![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/5/7/57f4d5d5caa001899d4bcaa509b80c92c567573d.png)

1. Then you can delete them. Save your view and reload your browser.