# \[BUG\] v8.1.5 AB Logix driver - Tags that are written and reset by PLC in 1 scan remain

**URL:** <https://forum.inductiveautomation.com/t/bug-v8-1-5-ab-logix-driver-tags-that-are-written-and-reset-by-plc-in-1-scan-remain/47378>\
**Category:** Ignition\
**Tags:** ignition81\
**Created:** [June 3, 2021, 2:19am UTC](https://forum.inductiveautomation.com/t/bug-v8-1-5-ab-logix-driver-tags-that-are-written-and-reset-by-plc-in-1-scan-remain/47378 "2021-06-03T02:19:07Z")\
**Posts on this page:** 1\
**Showing post:** 8

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [August 2, 2022, 11:34pm UTC](https://forum.inductiveautomation.com/t/bug-v8-1-5-ab-logix-driver-tags-that-are-written-and-reset-by-plc-in-1-scan-remain/47378/8 "2022-08-02T23:34:26Z")

</div>

It is a real race without read-after-write.

> [@Missing Gateway Tag Change Events](https://forum.inductiveautomation.com/t/missing-gateway-tag-change-events/62289/8):
>
> If the PLC is waiting for you to turn it off, and that is the only logic remaining, the PLC can turn it back on before OPC polling sees that you succeeded turning it off. If the process in the PLC is complex, natural delays might have the race only show up when comms are disturbed, so you might have never experienced it. And then it happens and you can’t explain it, because you don’t believe what you are doing is “wrong”.

Read-after-write shortens the interval, but if the logic is primed to clear instantly, it still won't help.

---

_[View the full topic](https://forum.inductiveautomation.com/t/bug-v8-1-5-ab-logix-driver-tags-that-are-written-and-reset-by-plc-in-1-scan-remain/47378)._