Hello,

I am very new to connecting a Siemens PLC to Ignition- I have connected it and am reading 1 boolean tag. I am trying to connect to a word tag that appears to be in a DB? I am not sure what the exact structure should be. The tag is DB50.DBW154.  
Any advice?

---

<div class="post-metadata">

**Author:** ![zxcslo](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/zxcslo/32/61610_2.png) [@zxcslo](https://forum.inductiveautomation.com/u/zxcslo)\
**Post date:** [May 27, 2023, 3:50am UTC](https://forum.inductiveautomation.com/t/calling-siemens-300-tags/74226/2 "2023-05-27T03:50:43Z")

</div>

[https://docs.inductiveautomation.com/display/DOC81/Siemens#Siemens-ConfiguringSiemensAddressing](https://docs.inductiveautomation.com/display/DOC81/Siemens#Siemens-ConfiguringSiemensAddressing)  
The syntax is: `[s7_300]DB50,W154` or `[s7_300]DB50,I154`

---

<div class="post-metadata">

**Author:** ![Tyler\_Esters1](https://avatars.discourse-cdn.com/v4/letter/t/278dde/32.png) [@Tyler\_Esters1](https://forum.inductiveautomation.com/u/Tyler_Esters1)\
**Post date:** [June 5, 2023, 3:16pm UTC](https://forum.inductiveautomation.com/t/calling-siemens-300-tags/74226/3 "2023-06-05T15:16:16Z")

</div>

I figured out the problem, the tag was simply DB50,i154. This was due to my lack of knowledge in Siemens S7 Navigation.