# Can Archestra use the SQL Bridge .modl?

**URL:** <https://forum.inductiveautomation.com/t/can-archestra-use-the-sql-bridge-modl/10109>\
**Category:** General Discussion\
**Created:** [June 9, 2015, 2:13pm UTC](https://forum.inductiveautomation.com/t/can-archestra-use-the-sql-bridge-modl/10109 "2015-06-09T14:13:58Z")\
**Posts on this page:** 4\
**Page:** 1

<div class="post-metadata">

**Author:** ![DSI600](https://avatars.discourse-cdn.com/v4/letter/d/ad7895/32.png) [@DSI600](https://forum.inductiveautomation.com/u/DSI600)\
**Post date:** [June 9, 2015, 2:13pm UTC](https://forum.inductiveautomation.com/t/can-archestra-use-the-sql-bridge-modl/10109/1 "2015-06-09T14:13:58Z")

</div>

We are using Archestra by Wonderware currently and was wondering if anyone has or knows if there is a way to have the SQL Bridge modl exposed to the Archestra .NET scripting. Only way I could think it could work is if we were able to wrap it up into a .dll and import it as a script function library.

Thanks -

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [June 9, 2015, 2:35pm UTC](https://forum.inductiveautomation.com/t/can-archestra-use-the-sql-bridge-modl/10109/2 "2015-06-09T14:35:44Z")

</div>

No, we don’t support anything like that.

---

<div class="post-metadata">

**Author:** ![DSI600](https://avatars.discourse-cdn.com/v4/letter/d/ad7895/32.png) [@DSI600](https://forum.inductiveautomation.com/u/DSI600)\
**Post date:** [December 17, 2018, 9:22pm UTC](https://forum.inductiveautomation.com/t/can-archestra-use-the-sql-bridge-modl/10109/3 "2018-12-17T21:22:22Z")

</div>

Just wanted to update this thread. I was able to get Archestra UDA members tied to SQL tags in Ignition and to send data to a named query to insert data into SQL utilizing the SQL Bridge module.

I setup the OI.Gateway in Wonderware and created a Archestra Connection, installed the OPC Core Components from the OPC foundation on this server, Installed Ignition on the same server as a test. I then setup Ignition with a OPC-DA COM Connection and pointed it to the Wonderware OI.Gateway. I could then create tags inside Ignition that attached to objects attributes in my galaxy. Can do full read / write from either the object viewer in Wonderware or Ignition and see the tags update both places.

Very cool!

---

<div class="post-metadata">

**Author:** ![tamerplc](https://avatars.discourse-cdn.com/v4/letter/t/d78d45/32.png) [@tamerplc](https://forum.inductiveautomation.com/u/tamerplc)\
**Post date:** [December 19, 2018, 5:54pm UTC](https://forum.inductiveautomation.com/t/can-archestra-use-the-sql-bridge-modl/10109/4 "2018-12-19T17:54:06Z")

</div>

I did same with WW MES system.  
This concept can be applied between ignition and any system acting as OPC client.  
Ignition have a very flexibility to deal with any system.  
This us the power ignition.