Using 8.1.44+ and the Mitsubishi driver with Q-series selected will allow communication with Keyence KV-series PLCs.

The following tables translate Keyence device (memory area) names to Mitsubishi.

 ![Screenshot 2025-02-18 at 13.24.35](https://us1.discourse-cdn.com/inductiveautomation/original/3X/2/1/21ac75833eb37dd8b11ccae0a67cb6b63bee67bc.png)  
 ![Screenshot 2025-02-18 at 13.24.44](https://us1.discourse-cdn.com/inductiveautomation/original/3X/9/2/92a30acdc39644c42b2e9fc9e6a43915c0841561.png)

---