I am running Ignition 7.8.2 on  
“Linux CCDebianCF 3.20-4-686-pae #1 SMP Debian 3.2.68-1+deb7u3 i686 GNU/Linux”

Simulator Devices:[https://ge.box.com/s/mbf895g29qflwn498o8adcth6gzlwile](https://ge.box.com/s/mbf895g29qflwn498o8adcth6gzlwile)

OPC UA setting [https://ge.box.com/s/by1fcptvo44fep4kp6qhsowg6qewjoe3](https://ge.box.com/s/by1fcptvo44fep4kp6qhsowg6qewjoe3)

OPC server connection [https://ge.box.com/s/r4fk5ff4eurgp5kphgpuxj0wexasu87x](https://ge.box.com/s/r4fk5ff4eurgp5kphgpuxj0wexasu87x)

Endpoint [https://ge.box.com/s/z5uz9gwm17gkw842vtvlutffrr5n1i7r](https://ge.box.com/s/z5uz9gwm17gkw842vtvlutffrr5n1i7r)

Error message: [https://ge.box.com/s/zafsv82duq31alo1kpt03e1xftgx4ak7](https://ge.box.com/s/zafsv82duq31alo1kpt03e1xftgx4ak7)

License: [https://ge.box.com/s/gwcw5gf3vplpxsenmx0fkw2ct0ajjgpb](https://ge.box.com/s/gwcw5gf3vplpxsenmx0fkw2ct0ajjgpb)

Is there anything missing during my configuration? I had tried to restart the gateway or OPC-UA module.

Thanks. Hope the image links above work or please refer the attachment.

Yongzhi

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [April 4, 2016, 5:23pm UTC](https://forum.inductiveautomation.com/t/cannot-browse-connection-ignition-opc-ua-server/11459/2 "2016-04-04T17:23:42Z")

</div>

Under the server settings, the “Endpoint Address” setting should just be the IP address of the machine you’re on. After setting it you’ll need to restart the gateway.

---

<div class="post-metadata">

**Author:** ![Yongzhi.Liu](https://avatars.discourse-cdn.com/v4/letter/y/9e8a1a/32.png) [@Yongzhi.Liu](https://forum.inductiveautomation.com/u/Yongzhi.Liu)\
**Post date:** [April 5, 2016, 2:10am UTC](https://forum.inductiveautomation.com/t/cannot-browse-connection-ignition-opc-ua-server/11459/3 "2016-04-05T02:10:36Z")

</div>

Thanks for the advice. The problem is still there.

OPC-UA \> Settings \> Server \> Endpoint Address \> changed to “opc.tcp://3.242.222.148”

OPC Connections \> Servers \> created a new name and description, authentication “opcuauser/password”

OPC Connections \> Servers \> OPC Server Connections \> endpoint \> Discover OPC-UA Endpoints \> “opc.tcp//3.242.222.148:4096”, check “opc.tcp//192.168.1.21:4096/iaopcua/None”

OPC-UA module restarted,  
Gateway restarted.

---

<div class="post-metadata">

**Author:** ![Yongzhi.Liu](https://avatars.discourse-cdn.com/v4/letter/y/9e8a1a/32.png) [@Yongzhi.Liu](https://forum.inductiveautomation.com/u/Yongzhi.Liu)\
**Post date:** [April 8, 2016, 3:19am UTC](https://forum.inductiveautomation.com/t/cannot-browse-connection-ignition-opc-ua-server/11459/4 "2016-04-08T03:19:23Z")

</div>

It is solved. There is a hidden router somewhere in my machine. The solution is  
1.OPC-UA -\> Settings -\> Server -\> Endpoint Address -\> 3.222.123.456 (IP address of my machine)  
2. OPC Connections -\> OPC Server Connections -\> endpoint -\> Discover OPC-UA Endpoint -\> opc.tcp://3.222.123.456:4096

Thanks all and Sam Ngeru.