# Cannot run prepared statement while gateway is in disconnect

**URL:** <https://forum.inductiveautomation.com/t/cannot-run-prepared-statement-while-gateway-is-in-disconnect/2374>\
**Category:** Archived Topics\
**Created:** [November 29, 2010, 3:56pm UTC](https://forum.inductiveautomation.com/t/cannot-run-prepared-statement-while-gateway-is-in-disconnect/2374 "2010-11-29T15:56:27Z")\
**Posts on this page:** 2\
**Page:** 1

<div class="post-metadata">

**Author:** ![alexr](https://avatars.discourse-cdn.com/v4/letter/a/8dc957/32.png) [@alexr](https://forum.inductiveautomation.com/u/alexr)\
**Post date:** [November 29, 2010, 3:56pm UTC](https://forum.inductiveautomation.com/t/cannot-run-prepared-statement-while-gateway-is-in-disconnect/2374/1 "2010-11-29T15:56:27Z")

</div>

Hi,

When I try to run any update sentence for SQL Server in preview mode from FactoryPMI Designer, appears me the next error:  
“Cannot run prepared statement while gateway is in disconnected or read-only mode”

Any idea?

Thanks

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [November 29, 2010, 4:10pm UTC](https://forum.inductiveautomation.com/t/cannot-run-prepared-statement-while-gateway-is-in-disconnect/2374/2 "2010-11-29T16:10:53Z")

</div>

Either your designer is disconnected from the gateway or you are in read-only mode 😛

[This is the user manual entry for Ignition on communication modes, but the same applies to legacy FPMI.](http://inductiveautomation.com/support/usermanuals/ignition/communication_modes.htm?zoom_highlightsub=read-only%2Bmode)

You need to switch the communication mode to Read/Write before you can run update queries.