# Cannot write to tags in a remote tag provider

**URL:** <https://forum.inductiveautomation.com/t/cannot-write-to-tags-in-a-remote-tag-provider/104646>\
**Category:** Ignition\
**Tags:** ignition81, edge\
**Created:** [April 3, 2025, 1:34pm UTC](https://forum.inductiveautomation.com/t/cannot-write-to-tags-in-a-remote-tag-provider/104646 "2025-04-03T13:34:15Z")\
**Posts on this page:** 2\
**Page:** 1

<div class="post-metadata">

**Author:** ![Alex\_Jaffe](https://avatars.discourse-cdn.com/v4/letter/a/ecccb3/32.png) [@Alex\_Jaffe](https://forum.inductiveautomation.com/u/Alex_Jaffe)\
**Post date:** [April 3, 2025, 1:34pm UTC](https://forum.inductiveautomation.com/t/cannot-write-to-tags-in-a-remote-tag-provider/104646/1 "2025-04-03T13:34:15Z")

</div>

I am using an ignition edge and a standard ignition gateway connected over a gateway network. there is a PLC connected to the edge and I have set up a remote tag provider on the ignition gateway and can see the remote tags. however i cannot write to them.

I checked both the Security Zones and Service Security in the main Ignition Gateway and as far as i can tell it is set up correctly (as shown below). Is there something i am missing? if so please let me know, thank you.  
Security Zone Setup

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/a/c/acc651351b367607af2fc45921abab97a9b0c05a.jpeg)

Service Security Setup (The blacked out name is the remote tag provider- it was inherited but i changed it to readwriteedit to see if that would fix it, it didn't)

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/f/7/f7be8b4ec3e0a9caf4a2d8185f4712b64cf43e92.jpeg)

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [April 3, 2025, 1:39pm UTC](https://forum.inductiveautomation.com/t/cannot-write-to-tags-in-a-remote-tag-provider/104646/2 "2025-04-03T13:39:11Z")

</div>

The Edge node also has to be configured to allow writes and/or edits from the standard gateway.