# Can't Clear Changed Alarm

**URL:** <https://forum.inductiveautomation.com/t/cant-clear-changed-alarm/64250>\
**Category:** Ignition\
**Tags:** ignition81, vision\
**Created:** [September 19, 2022, 9:09pm UTC](https://forum.inductiveautomation.com/t/cant-clear-changed-alarm/64250 "2022-09-19T21:09:42Z")\
**Posts on this page:** 9\
**Page:** 1

<div class="post-metadata">

**Author:** ![zacht](https://avatars.discourse-cdn.com/v4/letter/z/ea5d25/32.png) [@zacht](https://forum.inductiveautomation.com/u/zacht)\
**Post date:** [September 19, 2022, 9:09pm UTC](https://forum.inductiveautomation.com/t/cant-clear-changed-alarm/64250/1 "2022-09-19T21:09:42Z")

</div>

We had an alarm that had the alarm name of `10 Mix Tank Leak/Low` (Figure. 1). This displayed as ‘Low’ on the alarm status table, which might be a bug of its own. Recognizing that using a ‘/’ character in the name of a programming element was a terrible choice, I changed the name of the alarm to something more suitable. Now, however, the alarm refuses to clear, even though the tag it’s tied to has transitioned out of the alarm condition. How can I clear this alarm and get it off the alarm status table?

![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/c/5/c53e275f5aa0b2a79c91a67f202405bc49eaf34d.png)  
Figure 1. Relevant alarm configuration

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/e/4/e45fa5a151d5545a9ffc03200de77fc87c47cb69.png)  
Figure 2. Alarm status table display  
Ignition Version: 8.1.17

---

<div class="post-metadata">

**Author:** ![jlandwerlen](https://avatars.discourse-cdn.com/v4/letter/j/bc8723/32.png) [@jlandwerlen](https://forum.inductiveautomation.com/u/jlandwerlen)\
**Post date:** [September 19, 2022, 9:50pm UTC](https://forum.inductiveautomation.com/t/cant-clear-changed-alarm/64250/2 "2022-09-19T21:50:17Z")

</div>

You probably need to acknowledge, check `Ack Mode` - which is right below `Display Path`, my guess is that it is set to manual.

---

<div class="post-metadata">

**Author:** ![zacht](https://avatars.discourse-cdn.com/v4/letter/z/ea5d25/32.png) [@zacht](https://forum.inductiveautomation.com/u/zacht)\
**Post date:** [September 19, 2022, 9:59pm UTC](https://forum.inductiveautomation.com/t/cant-clear-changed-alarm/64250/3 "2022-09-19T21:59:07Z")

</div>

Ack mode is set to manual, but when the footer is enabled, the Acknowledge button is grayed out. I had a conversation with Support. They suggested I stop the gateway, delete `%Install Directory%/data/alarms_######`, then restart the gateway. I’ll try that next weekend and see if it helps.

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/c/8/c8d0d4b52735d0b63787f1f47dbabd34cb8929fa.png)

---

<div class="post-metadata">

**Author:** ![jlandwerlen](https://avatars.discourse-cdn.com/v4/letter/j/bc8723/32.png) [@jlandwerlen](https://forum.inductiveautomation.com/u/jlandwerlen)\
**Post date:** [September 19, 2022, 10:21pm UTC](https://forum.inductiveautomation.com/t/cant-clear-changed-alarm/64250/4 "2022-09-19T22:21:47Z")

</div>

Do any alarms allow acknowledge? If not, check extension function `isAcknowledgeEnabled`.

---

<div class="post-metadata">

**Author:** ![zacht](https://avatars.discourse-cdn.com/v4/letter/z/ea5d25/32.png) [@zacht](https://forum.inductiveautomation.com/u/zacht)\
**Post date:** [September 19, 2022, 10:28pm UTC](https://forum.inductiveautomation.com/t/cant-clear-changed-alarm/64250/5 "2022-09-19T22:28:02Z")

</div>

The extension function doesn’t seem to be enabled. I assume, based on the image, that the default behavior is to return True.

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/c/5/c5e9d99e91037ed8c2e2456b32400993bd511a0d.png)

---

<div class="post-metadata">

**Author:** ![jlandwerlen](https://avatars.discourse-cdn.com/v4/letter/j/bc8723/32.png) [@jlandwerlen](https://forum.inductiveautomation.com/u/jlandwerlen)\
**Post date:** [September 19, 2022, 10:37pm UTC](https://forum.inductiveautomation.com/t/cant-clear-changed-alarm/64250/6 "2022-09-19T22:37:36Z")

</div>

It is, you could also try setting the alarm high again. Otherwise yeah I guess wait and restart.

---

<div class="post-metadata">

**Author:** ![zacht](https://avatars.discourse-cdn.com/v4/letter/z/ea5d25/32.png) [@zacht](https://forum.inductiveautomation.com/u/zacht)\
**Post date:** [September 24, 2022, 6:08am UTC](https://forum.inductiveautomation.com/t/cant-clear-changed-alarm/64250/7 "2022-09-24T06:08:52Z")

</div>

> [@zacht](#):
>
> They suggested I stop the gateway, delete `%Install Directory%/data/alarms_######`, then restart the gateway.

I did this today while we were down and it solved the problem.

---

<div class="post-metadata">

**Author:** ![chaoliang](https://avatars.discourse-cdn.com/v4/letter/c/ba8739/32.png) [@chaoliang](https://forum.inductiveautomation.com/u/chaoliang)\
**Post date:** [October 18, 2022, 11:01pm UTC](https://forum.inductiveautomation.com/t/cant-clear-changed-alarm/64250/8 "2022-10-18T23:01:41Z")

</div>

Just checked the gateway.  
This file name has a . in front of this alarm name  
like ".alarms\_xxxxx".  
Is it right?

---

<div class="post-metadata">

**Author:** ![zacht](https://avatars.discourse-cdn.com/v4/letter/z/ea5d25/32.png) [@zacht](https://forum.inductiveautomation.com/u/zacht)\
**Post date:** [October 18, 2022, 11:04pm UTC](https://forum.inductiveautomation.com/t/cant-clear-changed-alarm/64250/9 "2022-10-18T23:04:06Z")

</div>

Yes. The filename on my system is `.alarms_1665927103842`.