<div class="post-metadata">

**Author:** ![Anna\_Goldberg](https://avatars.discourse-cdn.com/v4/letter/a/ecae2f/32.png) [@Anna\_Goldberg](https://forum.inductiveautomation.com/u/Anna_Goldberg)\
**Post date:** [December 12, 2022, 11:35am UTC](https://forum.inductiveautomation.com/t/cant-see-the-datablockinstance-dbs-in-opc-client/67491/1 "2022-12-12T11:35:28Z")

</div>

Hello, I have an issue with the OPC-UA client.  
I've configured an OPC-Server in SILMENS PLC S1500 and added an OPC connection to Ignition.  
When I open the quick client, I can read all tags configured as DataBlocksGlobal, all inputs etc., but I can't see any tags configured at DataBlocksInstance. When I try to open the folder it seems to be empty. In order to eliminate any configuration issues in Siemens, I've connected to it using a different OPC client and I saw the DataBlock instances.  
Maybe someone encountered the same issue?  
Would appreciate help on that.

---

<div class="post-metadata">

**Author:** ![Ayanna\_Brown](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/ayanna_brown/32/38406_2.png) [@Ayanna\_Brown](https://forum.inductiveautomation.com/u/Ayanna_Brown)\
**Post date:** [December 14, 2022, 9:51pm UTC](https://forum.inductiveautomation.com/t/cant-see-the-datablockinstance-dbs-in-opc-client/67491/2 "2022-12-14T21:51:01Z")

</div>

A support ticket has been made for this. Solution is to address the OPC tag manually in the Designer through the OPC Item path.

---

<div class="post-metadata">

**Author:** ![Anna\_Goldberg](https://avatars.discourse-cdn.com/v4/letter/a/ecae2f/32.png) [@Anna\_Goldberg](https://forum.inductiveautomation.com/u/Anna_Goldberg)\
**Post date:** [December 19, 2022, 11:10am UTC](https://forum.inductiveautomation.com/t/cant-see-the-datablockinstance-dbs-in-opc-client/67491/3 "2022-12-19T11:10:18Z")

</div>

Thanks