The connection you configured in UaExpert is using X509 authentication, not anonymous authentication. The key and certificate used for this mode of authentication is _not_ the same key and certificate used to secure the connection between client and server (the Application Instance Certificate).

Ignition’s OPC UA client _does not support_ X509 authentication. The advanced configuration option you uncovered is to allow a different Application Instance Certificate to be used by the connection.

If you want to establish an anonymous connection then simply leave the username and password fields blank. But this is _not_ what you did in UaExpert.

---