# Change Alarm Priority from Vision Window

**URL:** <https://forum.inductiveautomation.com/t/change-alarm-priority-from-vision-window/62647>\
**Category:** Ignition\
**Tags:** ignition81, vision\
**Created:** [August 3, 2022, 6:33pm UTC](https://forum.inductiveautomation.com/t/change-alarm-priority-from-vision-window/62647 "2022-08-03T18:33:15Z")\
**Posts on this page:** 2\
**Page:** 1

<div class="post-metadata">

**Author:** ![cole.young34](https://avatars.discourse-cdn.com/v4/letter/c/ee59a6/32.png) [@cole.young34](https://forum.inductiveautomation.com/u/cole.young34)\
**Post date:** [August 3, 2022, 6:33pm UTC](https://forum.inductiveautomation.com/t/change-alarm-priority-from-vision-window/62647/1 "2022-08-03T18:33:15Z")

</div>

Hi  
Is it possible to change the Priority of an alarm dynamically from a vision window? Everything that I have tried has given me an error stating “Bad\_Unsupported”  
Thanks

---

<div class="post-metadata">

**Author:** ![jlandwerlen](https://avatars.discourse-cdn.com/v4/letter/j/bc8723/32.png) [@jlandwerlen](https://forum.inductiveautomation.com/u/jlandwerlen)\
**Post date:** [August 3, 2022, 6:52pm UTC](https://forum.inductiveautomation.com/t/change-alarm-priority-from-vision-window/62647/2 "2022-08-03T18:52:22Z")

</div>

You can use `system.tag.configure`. There is an example on interacting with alarms near the bottom.

[https://docs.inductiveautomation.com/display/DOC81/system.tag.configure](https://docs.inductiveautomation.com/display/DOC81/system.tag.configure)

Note, that doing this will set overrides for the entire alarm.