# Click PLC Communication with Ignition

**URL:** <https://forum.inductiveautomation.com/t/click-plc-communication-with-ignition/86696>\
**Category:** Ignition\
**Created:** [March 1, 2024, 7:43pm UTC](https://forum.inductiveautomation.com/t/click-plc-communication-with-ignition/86696 "2024-03-01T19:43:26Z")\
**Posts on this page:** 1\
**Showing post:** 5

<div class="post-metadata">

**Author:** ![bkarabinchak.psi](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/bkarabinchak.psi/32/83567_2.png) [@bkarabinchak.psi](https://forum.inductiveautomation.com/u/bkarabinchak.psi)\
**Post date:** [March 1, 2024, 7:51pm UTC](https://forum.inductiveautomation.com/t/click-plc-communication-with-ignition/86696/5 "2024-03-01T19:51:26Z")

</div>

Can you ping the CLICK from the Ignition gateway? Did you setup your addresses in the ModBus TCP? Note that you need to drop 0,1,3, or 4 from the beginning of your address that is handled when you select the register type -[Connecting to Click PLC for tags?](https://forum.inductiveautomation.com/t/connecting-to-click-plc-for-tags/48117)

---

_[View the full topic](https://forum.inductiveautomation.com/t/click-plc-communication-with-ignition/86696)._