# Click PLC Modus TCP weird data

**URL:** <https://forum.inductiveautomation.com/t/click-plc-modus-tcp-weird-data/63346>\
**Category:** Ignition\
**Created:** [August 23, 2022, 8:02pm UTC](https://forum.inductiveautomation.com/t/click-plc-modus-tcp-weird-data/63346 "2022-08-23T20:02:45Z")\
**Posts on this page:** 5\
**Page:** 1

<div class="post-metadata">

**Author:** ![Jim\_Tennant](https://avatars.discourse-cdn.com/v4/letter/j/74df32/32.png) [@Jim\_Tennant](https://forum.inductiveautomation.com/u/Jim_Tennant)\
**Post date:** [August 23, 2022, 8:02pm UTC](https://forum.inductiveautomation.com/t/click-plc-modus-tcp-weird-data/63346/1 "2022-08-23T20:02:45Z")

</div>

Hi everyone I’m new to ignition and have run into a weird problem.

I am using a click plc connected via modbus tcp with two analog sensors… data outputs as a float between 0 and 100.

However on the ignition side of things my outputs are in the thousands. What am I doing wrong? Figured it was a datatype issue but trying a few didnt help.

The values start around 16500 and go to 17100ish, not sure if that helps at all.

Here are some pics for troubleshooting.

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/8/e/8e17d58f7590be1741b27dc49898d5bb8c5949a3.png)  
 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/d/a/dab3803fc6d3b8ead53f2cee0709d031ebde204f.png)  
 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/a/d/add4464d73c82894f88ffb5dceb3b0163f099623.png)

---

<div class="post-metadata">

**Author:** ![Matrix\_Engineering](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/matrix_engineering/32/19781_2.png) [@Matrix\_Engineering](https://forum.inductiveautomation.com/u/Matrix_Engineering)\
**Post date:** [August 23, 2022, 8:15pm UTC](https://forum.inductiveautomation.com/t/click-plc-modus-tcp-weird-data/63346/2 "2022-08-23T20:15:11Z")

</div>

Welcome!

1. Drop the first digit (in Ignition, 28673) (You’ve done this, posting for anyone else that finds this thread).
2. It’s a float, so HRF28673
3. Check reverse word order (Gateway/config/device connections/Click PLC… Advanced properties)
4. Check one-based (think 8.1 now calls this zero-based) option (found in same place as #3)

---

<div class="post-metadata">

**Author:** ![zacht](https://avatars.discourse-cdn.com/v4/letter/z/ea5d25/32.png) [@zacht](https://forum.inductiveautomation.com/u/zacht)\
**Post date:** [August 23, 2022, 8:18pm UTC](https://forum.inductiveautomation.com/t/click-plc-modus-tcp-weird-data/63346/3 "2022-08-23T20:18:47Z")

</div>

Also look at the section on Unit ID on this page.  
[https://docs.inductiveautomation.com/display/DOC81/Modbus+Addressing](https://docs.inductiveautomation.com/display/DOC81/Modbus+Addressing)

---

<div class="post-metadata">

**Author:** ![Jim\_Tennant](https://avatars.discourse-cdn.com/v4/letter/j/74df32/32.png) [@Jim\_Tennant](https://forum.inductiveautomation.com/u/Jim_Tennant)\
**Post date:** [August 23, 2022, 8:22pm UTC](https://forum.inductiveautomation.com/t/click-plc-modus-tcp-weird-data/63346/4 "2022-08-23T20:22:41Z")

</div>

Ahh it was HRF!! Thanks a ton!

Also for anyone in the future I had to set the zero based to true.

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/e/6/e621bb0b652cb942804ce2a8cd7ecbda3865ad69.png)

---

<div class="post-metadata">

**Author:** ![Matrix\_Engineering](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/matrix_engineering/32/19781_2.png) [@Matrix\_Engineering](https://forum.inductiveautomation.com/u/Matrix_Engineering)\
**Post date:** [August 23, 2022, 8:28pm UTC](https://forum.inductiveautomation.com/t/click-plc-modus-tcp-weird-data/63346/5 "2022-08-23T20:28:21Z")

</div>

Glad you got sorted.

This manual page covers the different prefix:

[https://docs.inductiveautomation.com/display/DOC81/Modbus+Addressing](https://docs.inductiveautomation.com/display/DOC81/Modbus+Addressing)

I use Click and also Productivity. Don’t hesitate to ask if you’re stuck again!