# Clock Drift from PLC Timeout?

**URL:** <https://forum.inductiveautomation.com/t/clock-drift-from-plc-timeout/105933>\
**Category:** Ignition\
**Created:** [May 6, 2025, 6:34pm UTC](https://forum.inductiveautomation.com/t/clock-drift-from-plc-timeout/105933 "2025-05-06T18:34:54Z")\
**Posts on this page:** 16\
**Page:** 1

<div class="post-metadata">

**Author:** ![jacob\_geers](https://avatars.discourse-cdn.com/v4/letter/j/4da419/32.png) [@jacob\_geers](https://forum.inductiveautomation.com/u/jacob_geers)\
**Post date:** [May 6, 2025, 6:34pm UTC](https://forum.inductiveautomation.com/t/clock-drift-from-plc-timeout/105933/1 "2025-05-06T18:34:54Z")

</div>

Hello,

Looking for input on how to troubleshoot clock drift. We get several in a row occasionally but the CPU never spikes - is this a concern?

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/5/f/5f9f34d701c1cf5c4ef19e633a96f2b8ab933225.png)  
 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/f/5/f5ff69b34130fa2d51090207ff234591985c16df.png)

Based on the logs I notice we also get ABMicroLogixReadRequest warnings - could this be the issue? How do I go about troubleshooting? The two database issue are embarrasing but I don't think they are related.

**Example #1**

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/4/4/449bd28e6738ee2c5534e0afc1ce41c4ef8fac9e.png)

**Example #2**

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/d/0/d0fc039ac7a0a49ed64191b6e04a84bdb823ce71.png)

---

<div class="post-metadata">

**Author:** ![jacob\_geers](https://avatars.discourse-cdn.com/v4/letter/j/4da419/32.png) [@jacob\_geers](https://forum.inductiveautomation.com/u/jacob_geers)\
**Post date:** [May 6, 2025, 6:48pm UTC](https://forum.inductiveautomation.com/t/clock-drift-from-plc-timeout/105933/2 "2025-05-06T18:48:20Z")

</div>

Seems to always be these devices.

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/f/1/f194b7f6c326047644f6226a67b59bafdc2b3d5c.png)

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [May 6, 2025, 6:57pm UTC](https://forum.inductiveautomation.com/t/clock-drift-from-plc-timeout/105933/3 "2025-05-06T18:57:45Z")

</div>

It's most likely the other way around - these timeouts are caused by the clock drift.

---

<div class="post-metadata">

**Author:** ![jacob\_geers](https://avatars.discourse-cdn.com/v4/letter/j/4da419/32.png) [@jacob\_geers](https://forum.inductiveautomation.com/u/jacob_geers)\
**Post date:** [May 6, 2025, 8:20pm UTC](https://forum.inductiveautomation.com/t/clock-drift-from-plc-timeout/105933/4 "2025-05-06T20:20:33Z")

</div>

Is clock drift without high CPU a concern?

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [May 6, 2025, 8:25pm UTC](https://forum.inductiveautomation.com/t/clock-drift-from-plc-timeout/105933/5 "2025-05-06T20:25:55Z")

</div>

Yes, it can screw up history and typically indicates either untuned Java garbage collection or, in Windows, actual clock warps.

Consider adding the following to your `ignition.conf` file (with unique sequence numbers):

```python
wrapper.java.additional.10=-XX:+UseG1GC
wrapper.java.additional.11=-XX:MaxGCPauseMillis=25
wrapper.java.additional.12=-Xlog:gc:file=logs/gc.log:t,tags:filecount=5,filesize=4M
wrapper.java.additional.13=-XX:-OmitStackTraceInFastThrow

```

Restart your gateway and then watch the contents of the `gc.log` files.

If you are getting actual "pause-the-world" halts of \> ~100ms, you should look for memory usage problems.

---

<div class="post-metadata">

**Author:** ![jacob\_geers](https://avatars.discourse-cdn.com/v4/letter/j/4da419/32.png) [@jacob\_geers](https://forum.inductiveautomation.com/u/jacob_geers)\
**Post date:** [May 7, 2025, 3:04pm UTC](https://forum.inductiveautomation.com/t/clock-drift-from-plc-timeout/105933/6 "2025-05-07T15:04:47Z")

</div>

Thanks, will try over the weekend. Here is something that may be interesting, `gateway-shared-exec-engine` taking 20% of CPU when the clock drifts occur?

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/2/4/2421cd1ac14fbe529e8caa4de286bfbeccd4b753.png)

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [May 7, 2025, 3:10pm UTC](https://forum.inductiveautomation.com/t/clock-drift-from-plc-timeout/105933/7 "2025-05-07T15:10:00Z")

</div>

Might be interesting, you would need to stack trace from that thread (click the "+" button to expand) to know any more. It will probably be tricky to get a snapshot of that thread exactly when the CPU usage is high and the clock drift is happening.

---

<div class="post-metadata">

**Author:** ![Clancy\_Cavanaugh](https://avatars.discourse-cdn.com/v4/letter/c/45deac/32.png) [@Clancy\_Cavanaugh](https://forum.inductiveautomation.com/u/Clancy_Cavanaugh)\
**Post date:** [May 7, 2025, 3:22pm UTC](https://forum.inductiveautomation.com/t/clock-drift-from-plc-timeout/105933/8 "2025-05-07T15:22:06Z")

</div>

Are you on a 3 year old minor version by chance? I remember something similar occurring on our system a few years ago.

Our issue was caused by PLCs being powered off for maintenance, and Ignition appeared to be tying up threads waiting for the timeout. I believe it was fixed in version 8.1.15 though.

---

<div class="post-metadata">

**Author:** ![jacob\_geers](https://avatars.discourse-cdn.com/v4/letter/j/4da419/32.png) [@jacob\_geers](https://forum.inductiveautomation.com/u/jacob_geers)\
**Post date:** [May 7, 2025, 3:56pm UTC](https://forum.inductiveautomation.com/t/clock-drift-from-plc-timeout/105933/9 "2025-05-07T15:56:27Z")

</div>

Here is a thread dump with one item using 17% during the time of clock drifts, but it is different than before.  
[site-dev\_thread\_dump20250507-115452.json](https://forum.inductiveautomation.com/uploads/short-url/cswR0HNPTwK1EKhRRqMhc9sV2DZ.json) (531.9 KB)

---

<div class="post-metadata">

**Author:** ![jacob\_geers](https://avatars.discourse-cdn.com/v4/letter/j/4da419/32.png) [@jacob\_geers](https://forum.inductiveautomation.com/u/jacob_geers)\
**Post date:** [May 7, 2025, 3:57pm UTC](https://forum.inductiveautomation.com/t/clock-drift-from-plc-timeout/105933/10 "2025-05-07T15:57:18Z")

</div>

We are on 8.1.32.

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/c/5/c5738ef8ffd6deee7cc77a5c400490465312c4b3.png)

---

<div class="post-metadata">

**Author:** ![jacob\_geers](https://avatars.discourse-cdn.com/v4/letter/j/4da419/32.png) [@jacob\_geers](https://forum.inductiveautomation.com/u/jacob_geers)\
**Post date:** [May 8, 2025, 1:34pm UTC](https://forum.inductiveautomation.com/t/clock-drift-from-plc-timeout/105933/11 "2025-05-08T13:34:03Z")

</div>

Thanks, we ended up applying those gateway config changes.

12:07 5/28 - apply config change and restart service  
... no clock drifts  
00:24 5/29 - first clock drift  
... a few clock drifts  
5:51 5/29 - tons of clock drifts all hour

Attached is the gc.log file if you wouldn't mind taking a look? My team and I are now playing around with Visual VM but don't have much experience with it.  
[gc.log](https://forum.inductiveautomation.com/uploads/short-url/vqNeo0CVqxQQPJRhelG761mlus6.log) (1.5 MB)

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [May 8, 2025, 1:48pm UTC](https://forum.inductiveautomation.com/t/clock-drift-from-plc-timeout/105933/12 "2025-05-08T13:48:32Z")

</div>

You do not have a GC problem. There's no pause greater than 200ms in the entire log.

Which means you have a workload problem. You will need to study regular thread dumps and extra thread dumps when the problems start. (This can be quite time consuming--you probably want IA support involved.)

In my experience, this is often caused by mishandling of long-lived asynchronous threads.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [May 8, 2025, 1:49pm UTC](https://forum.inductiveautomation.com/t/clock-drift-from-plc-timeout/105933/13 "2025-05-08T13:49:22Z")

</div>

Is your Ignition Gateway running on real hardware or in a VM?

---

<div class="post-metadata">

**Author:** ![jacob\_geers](https://avatars.discourse-cdn.com/v4/letter/j/4da419/32.png) [@jacob\_geers](https://forum.inductiveautomation.com/u/jacob_geers)\
**Post date:** [May 8, 2025, 2:02pm UTC](https://forum.inductiveautomation.com/t/clock-drift-from-plc-timeout/105933/14 "2025-05-08T14:02:10Z")

</div>

VMware ESXi 8.0.3.

I will monitor threads on my own for awhile then make a support request. Thank you both very much!

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [May 8, 2025, 2:04pm UTC](https://forum.inductiveautomation.com/t/clock-drift-from-plc-timeout/105933/15 "2025-05-08T14:04:11Z")

</div>

> [@jacob\_geers](#):
>
> VMware

Ewww!

Have you followed all of the IA guidance on setting low latency mode and avoiding overcommitted resources? (VMware is poorly configured by default for latency-sensitive applications like Ignition.)

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [May 8, 2025, 2:05pm UTC](https://forum.inductiveautomation.com/t/clock-drift-from-plc-timeout/105933/16 "2025-05-08T14:05:20Z")

</div>

[https://support.inductiveautomation.com/hc/en-us/articles/12888090388237-Considerations-and-Best-Practices-for-VMs-Hosting-Ignition](https://support.inductiveautomation.com/hc/en-us/articles/12888090388237-Considerations-and-Best-Practices-for-VMs-Hosting-Ignition)