I am not able to see my coil tag values in the OPC Quick Client section.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [March 24, 2021, 8:38pm UTC](https://forum.inductiveautomation.com/t/coil-modbus-tags/44875/2 "2021-03-24T20:38:28Z")

</div>

Have you created an [address mapping](https://docs.inductiveautomation.com/display/DOC81/Modbus+Address+Mapping)?

Or just created tags in the Ignition Designer? Or neither?

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [March 24, 2021, 8:38pm UTC](https://forum.inductiveautomation.com/t/coil-modbus-tags/44875/3 "2021-03-24T20:38:35Z")

</div>

Ignition’s native Modbus driver doesn’t offer built-in browsing. Did you define aliases for the coils?

If you want to be able to browse your Modbus device, you might consider my alternate driver:

[http://forum.inductiveautomation.com/t/automation-professionals-advanced-modbus-driver/41312/16](http://forum.inductiveautomation.com/t/automation-professionals-advanced-modbus-driver/41312/16)