I’m writing the item path for coils directly on the designer like for example [MyDevice]C50 but I’m not getting any value from it, I have this converter where the value of the Koyo PLC can be converted from Koyo to Modbus values  
how can I write the equivalent of the C50 in modbus like for example C50 is equivalent to 3113 in modbus, do i just write it like [MyDevice]C3113?

---

<div class="post-metadata">

**Author:** ![greg.simpson](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/greg.simpson/32/3135_2.png) [@greg.simpson](https://forum.inductiveautomation.com/u/greg.simpson)\
**Post date:** [February 5, 2013, 5:20pm UTC](https://forum.inductiveautomation.com/t/coils/5803/2 "2013-02-05T17:20:33Z")

</div>

That is correct, it would be C and then the coil that you would like to read. So, just like your example of  
[MyDevice]C3113.

Check out the Modbus Specific Addressing section of our user manual for more information  
[inductiveautomation.com/support/ … essing.htm](http://inductiveautomation.com/support/usermanuals/ignition/addressing.htm)

---

<div class="post-metadata">

**Author:** ![cacordova](https://avatars.discourse-cdn.com/v4/letter/c/bbce88/32.png) [@cacordova](https://forum.inductiveautomation.com/u/cacordova)\
**Post date:** [February 5, 2013, 5:30pm UTC](https://forum.inductiveautomation.com/t/coils/5803/3 "2013-02-05T17:30:38Z")

</div>

ok thank you 🙂