I had a PLC (CompactLogix) go offline for a while. When it came back Ignition was not able to connect. Here are some reoccuring error from the console:

-Unknown RequestId: 345571  
-Reaper found timed-out operation: PublishRequest RequestId=460635 RequestHandle=460416  
-Reaper found timed-out operation: PublishRequest RequestId=460634 RequestHandle=460415  
-Reaper found timed-out operation: PublishRequest RequestId=460636 RequestHandle=460417  
-Unknown RequestId: 345570

In the Configuration section, under Devices, that device always says “Browse Pending”. I am currently running Ignition version 7.2.4.

I can ping the PLC as well as go online with RsLogix. Any ideas?

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [April 1, 2011, 4:39pm UTC](https://forum.inductiveautomation.com/t/compactlogix-stuck-on-browse-pending/2832/2 "2011-04-01T16:39:23Z")

</div>

Those messages aren’t related to the device not reconnecting, but:

If the system is still in that state and you can call into support so we can look at it that would be best.

Otherwise,

Does clicking [refresh browse] and waiting for it to finish work?  
If you edit, make no changes, and save (forces a reconnect), does that work?