Hello.

1. I have a question about Ignition redundancy. When switching from the master Ignition to the standby Ignition, it takes about 2 minutes for the gateway to fully transition. Are there any settings that can reduce this time?

2. The transition from standby back to master is very quick, taking about 20 seconds. What is the reason for this difference?

I would appreciate your response.

---

<div class="post-metadata">

**Author:** ![jlandwerlen](https://avatars.discourse-cdn.com/v4/letter/j/bc8723/32.png) [@jlandwerlen](https://forum.inductiveautomation.com/u/jlandwerlen)\
**Post date:** [November 25, 2024, 1:11am UTC](https://forum.inductiveautomation.com/t/comparative-analysis-of-master-and-standby-transition-times/99049/2 "2024-11-25T01:11:05Z")

</div>

You can try changing standby level to warm.

> **[Setting Up Redundancy | Ignition User Manual](https://docs.inductiveautomation.com/docs/8.1/platform/ignition-redundancy/setting-up-redundancy#redundancy-settings)**
>
> In redundancy, both nodes will share the exact same configuration state. When a Backup node connects to a Master node, the Backup will attempt to synchronize itself with the Master. Therefore, before you set up for redundancy the following should be...

---

<div class="post-metadata">

**Author:** ![WOOSEUNG\_KIM](https://avatars.discourse-cdn.com/v4/letter/w/e99b99/32.png) [@WOOSEUNG\_KIM](https://forum.inductiveautomation.com/u/WOOSEUNG_KIM)\
**Post date:** [November 25, 2024, 9:25am UTC](https://forum.inductiveautomation.com/t/comparative-analysis-of-master-and-standby-transition-times/99049/3 "2024-11-25T09:25:18Z")

</div>

I see that I didn't mention how I set it up before asking the question. I am asking about the status after setting standby to warm.

Current settings:  
[master]

Network Bind Interface: 10.20.52.51  
Master Node Address: 10.20.52.51  
[backup]

Network Bind Interface: 10.20.52.53  
Master Node Address: 10.20.52.51